few questions about how to program numerous groups scenario

Discussion in 'C-Bus Toolkit and C-Gate Software' started by yecora, Jun 17, 2011.

  1. yecora

    yecora

    Joined:
    Apr 6, 2011
    Messages:
    12
    Likes Received:
    0
    Location:
    Moscow, Russia
    I apologize in advance for possible obvious questions but I searched out forums and did'n get answer, so if there exist tech paper or manual I will be glad to read it - just point me on it.

    I'm programming a whole house lighting control with c-bus, system spec:

    4 12-channels relay modules
    2 4-channels dimmer modules
    7 DLT keypads
    about 30 4-buttons saturn keypads
    PC RS-232 interface as well.

    Problem - keypad modules is not able to handle scenario like "all off" because maximum amount of light groups that could be included in scenario is only 40. In my case I should turn off about 56 groups.

    I divide house on few zones - like 1 floor, 2 floor - in this case I can use Trigger on/off, but it works somehow strange - I can use only 1 trigger button per keypad and I can't put a custom DLT label on this action on DLT keypad.

    Also next strange point - If I program room within same floor - I use 1 trigger group but different actions - and activating any of these actions causes to trigger the whole group - looks like - 2 children rooms on the floor, 2 different buttons on different keypads, each button switches off all groups in each room. But status LEDs under those buttons work not obvious - like if I turn off boy's room - scene "Boy's room off" is ON and LED under that button also goes ON, after that I push button on next keypad, corresponding to "Girl's room OFF" - and LED under this button goes ON, but previous LED turns OFF. How usually this situation solves?

    I'm sorry again, looks like I just can't make a obvious thing, and I'm sure that underwritten problems could be solved easily - just point me in right direction, please.

    Oleg
     
    yecora, Jun 17, 2011
    #1
  2. yecora

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    For information about scenes, read this post

    If this does not answer your questions, let us know.

    Just put half of the scene in a different unit and use the same trigger group and action selector in both units. This way, both halves of the scene will occur together.
     
    Darren, Jun 18, 2011
    #2
  3. yecora

    yecora

    Joined:
    Apr 6, 2011
    Messages:
    12
    Likes Received:
    0
    Location:
    Moscow, Russia
    I read that topic and some questions remain. There was described a recommendation to use separate trigger group per each unit - to be sure that indicators on this unit will work correctly. But how I can manage situation when I have more then one keypad in one zone? One inside the room and one outside, and I have to operate with them not only scenes within this room? Ok, I can use external keypad's trigger but this trigger will break up indicators on another panels. A little bit messy. Well, I try to do it more precisely today anyway.

    And a one more question - why I cant put a label on a DLT panel' button when I put a trigger action on this button? It just do not storing.
     
    Last edited by a moderator: Jun 18, 2011
    yecora, Jun 18, 2011
    #3
  4. yecora

    Jasp

    Joined:
    May 25, 2010
    Messages:
    24
    Likes Received:
    0
    Location:
    Melbourne
    If you have more than one DLT for a room, then use the same trigger remote, that way your indicators should be in sync when the scene is on/off.

    For DLT Labels, just create an action selector for the DLT, this will allow you to name the button when a scene is used.
     
    Jasp, Jun 18, 2011
    #4
  5. yecora

    yecora

    Joined:
    Apr 6, 2011
    Messages:
    12
    Likes Received:
    0
    Location:
    Moscow, Russia
    small update

    Actually I did almost all things I wanted to do, so I hope my client will be happy with clipsal, but as russians usually say in such cases - "Spoons were found, but memory remains".

    So, just trying to figure out what was wrong with me or with clipsal hardware.

    Firs of all - scenes. I had to create a scene "All Off" which should be activated when owner leaves house and nobody stays there. Total amount of lighting groups - 56, so it wasn't possible to put all of them into one keypad's scene. I created a Trigger Group "All Off", and separated 56 groups between 2 keypads on 2 scenes and put them on "Virtual key". Both scenes was rewarded same action trigger "House off". On one of these keypads I created a trigger key which activated action trigger "House off". Detailed procedure (saturn keypad) - I set secondary application "Trigger", clicked on "P" on left, it converted to "S", set Group to "All Off", set Function to Trigger 1 and choose action trigger "House Off". That was uploaded and worked great. After that I tried to repeat absolutely the same at second keypad. It didn't work. So - WHY? Different action (toggle light group on same button worked fine). Well, I used after that Trigger 2 instead of Trigger 1 - same result. No response at all.

    Second point which put me in confusion - when I assigned traditional scene on a button - I wasn't able to put a Long Press action to call it. It shoud be very common - calling a scene not just as sudden press, so WHY? Or HOW it could be done?
     
    yecora, Jun 25, 2011
    #5
  6. yecora

    yecora

    Joined:
    Apr 6, 2011
    Messages:
    12
    Likes Received:
    0
    Location:
    Moscow, Russia
    And one last (i guess) question - client just reported me about some sudden actions - some groups suddenly turns on. What could do that?
     
    yecora, Jul 9, 2011
    #6
  7. yecora

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Whenever events occur on a C-Bus system that you don't understand, the first thing to do is connect the C-Bus Diagnostic utility to a PCI on the network and log the network traffic. Make sure time stamps are turned on.

    When the client reports that something unexpected has happened at a particular time you can then look through the log to see which C-Bus unit generated this message. This will help you to track down the problem and usually reveals a programming issue.
     
    Newman, Jul 10, 2011