Will a 5512RFVP run without Power?

Discussion in 'C-Bus Wired Hardware' started by Greg Mortlock, Jun 8, 2005.

  1. Greg Mortlock

    Greg Mortlock

    Joined:
    Aug 3, 2004
    Messages:
    10
    Likes Received:
    0
    I've a 110V project where I'll be installing a LE5504TD2A (a 110V version dimmer). Can I run a 240V 5512RFVP powered off the dimmer via the network, with no power connection to the relay, or must I use a 110V relay unit with it's power hooked up?
     
    Greg Mortlock, Jun 8, 2005
    #1
  2. Greg Mortlock

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    You will have to use a 110V Relay unit with it's power hooked up.

    When connected to C-Bus with no mains connection only the C-Bus micro and essential peripherals are powered. This is to allow programming of the unit without a mains connection. The power for operating the relays is derived from the mains input connection on the unit and with out that being present the relays won't switch.
     
    Newman, Jun 8, 2005
    #2
  3. Greg Mortlock

    Greg Mortlock

    Joined:
    Aug 3, 2004
    Messages:
    10
    Likes Received:
    0
    Ok, thanks. Figured that might be the case but couldn't tell from the manual.
     