Unusual DALI Fault – C-Bus to DALI Gateway / Loss of Control on 3 Fittings

Discussion in 'General Discussion' started by Lighting Auto, Nov 24, 2026 at 4:42 AM.

  1. Lighting Auto

    Lighting Auto

    Joined:
    Jul 8, 2018
    Messages:
    14
    Likes Received:
    0
    This is one of the strangest DALI faults I’ve encountered in recent years, and I’m interested to hear whether any other installers or integrators have experienced something similar or can suggest further tests.

    Background

    The site was originally commissioned in 2010 and uses a site-wide C-Bus lighting control system, with C-Bus to DALI gateways controlling the DALI fittings.

    The electrical contractor has been progressively upgrading the lighting from recessed PL fluorescent fittings to LED, along with a small number of suspended LED pendants.

    I’ve commissioned approximately 250 fittings back onto their respective DALI networks throughout the project, with everything going smoothly until the final stage.

    The last part of the project involved replacing six suspended pendants. These originally contained DALI-controlled circular fluorescent lamps, which are now obsolete.

    The DALI line in question has approximately 55 fittings, all of which were operating correctly before the contractor replaced the six pendants.

    Commissioning procedure and the fault

    I used Tridonic Master Configurator software, together with a Tridonic DALI power supply and USB-to-DALI interface, to address and assign the fittings to their correct groups.

    As I have done successfully for many years, I carried out this work using my own independent DALI power supply. This means my commissioning equipment was completely isolated from the building’s existing DALI power supplys.

    With the DALI line connected to my Tridonic USB interface and power supply, all fittings operate correctly. Every fitting responds as expected, and all groups switch correctly.

    However, as soon as I disconnect my commissioning equipment and reconnect the DALI line to the building’s original DALI power supply, three of the six new suspended pendants (within a group of five) simply cannot be controlled locked on at 100%.

    This is particularly puzzling because everything works perfectly when using my independent DALI tridonic power supply and tridonic USB interface.

    Investigation so far

    The electrical contractor has spent considerable time investigating the problem. The following work has been carried out:

    1. Replaced one DALI driver and swapped the DALI drivers between the three affected fittings. This made no difference.

    2. Investigated the DALI cabling and found a screw penetrating one of the cables.

    3. Checked the existing DALI cable and discovered that one of the DALI conductors appears to be using the earth conductor in the cable termination. I wasn’t particularly happy with the look of this arrangement, although I’m not certain whether this has since been corrected.

    4. I suggested disconnecting the section of the DALI circuit supplying the affected fittings and running new cabling. Unfortunately, this isn’t physically possible because the existing cabling runs through conduits cast into concrete beams.

    There has also been an additional development.

    The contractor rewired another group of six recessed fittings. These fittings were initially operating correctly after my commissioning work but subsequently started failing to turn off.

    My suspicion is that, during their investigation of the DALI cabling, they may have inadvertently connected this section of the circuit to the part of the DALI network experiencing the original problem.

    My current theories

    At this stage, I have two main suspicions:

    1. Cross-connection between two DALI circuits

    One conductor from each of two separate DALI lines may have inadvertently become interconnected somewhere in the installation.

    2. One DALI conductor is connected to earth or another grounded component

    There may be an unintended connection between one of the DALI conductors and an earthed component somewhere in the building.

    The fact that everything operates correctly when using my completely independent Tridonic DALI power supply, but fails when connected to the building’s original DALI power supply, makes me particularly suspicious of an external wiring or earthing issue.

    I have already disconnected the two DALI lines that I believe are adjacent to each other and measured each conductor against earth and against the other conductor. I couldn’t identify any cross-connections or continuity to earth during those tests.

    Next steps

    I’m returning to site to disconnect all the DALI lines on this floor and carry out the same tests individually.

    My initial assumptions about which DALI circuits run where were based on the apparent layout of the installation. However, given the age of the installation and the fact that some of the original cabling work from 2010 isn’t particularly tidy, I think it’s worth checking every circuit rather than making assumptions about the cable routes.

    It’s worth emphasising that the original DALI installation has operated virtually faultlessly for the past 16 years. This problem has only appeared following the replacement of the six suspended pendants.

    Has anyone experienced anything similar?

    I’d be particularly interested to hear from anyone who has encountered:

    ● DALI fittings that operate perfectly when powered from an independent DALI commissioning supply but fail when reconnected to the building’s DALI power supply.

    ● Unexpected interactions between two DALI lines, particularly where one conductor has become interconnected.

    ● DALI communication problems caused by an unintended connection between a DALI conductor and earth.

    ● Any unusual behaviour caused by multiple DALI power supplies or potential differences between DALI circuits.

    Are there any other tests or potential causes that you would investigate?

    I’m particularly interested in anything that might explain why the three new pendants work perfectly on my independent Tridonic supply but not on the original building supply.

    Any suggestions or experiences would be greatly appreciated.
     
    Lighting Auto, Nov 24, 2026 at 4:42 AM