touch screen no power

Discussion in 'General Discussion' started by Davo1, Mar 21, 2022.

  1. Davo1

    Davo1

    Joined:
    Mar 21, 2022
    Messages:
    1
    Likes Received:
    0
    I have inherited a CBus2 withSC5000ST touch screen which doesnt power up anymore. Also we can only turn lights on manually from main control panel as the wall switches/buttons don't light up or work.
     
    Davo1, Mar 21, 2022
    #1
  2. Davo1

    Wonkey

    Joined:
    Aug 3, 2004
    Messages:
    477
    Likes Received:
    50
    Location:
    Adelaide
    Check what voltage you have on the Pink cat 5 and is the C-Bus light ON, on the output units
     
    Wonkey, Mar 21, 2022
    #2
  3. Davo1

    Trevor

    Joined:
    Nov 22, 2018
    Messages:
    488
    Likes Received:
    42
    Location:
    Melbourne Victoria
    You should be getting about 20-30 volts on the cbus cable, if not it is most likely a dimmer or relay power supply problem. If it's not the above you can try disconnecting devices until the system comes good, indicating the bad one.

    regards
    Trevor
     
    Trevor, Mar 22, 2022
    #3
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.