Temperature sensor shows high

Discussion in 'C-Bus Wired Hardware' started by nickrusanov, Sep 8, 2004.

  1. nickrusanov

    nickrusanov

    Joined:
    Aug 5, 2004
    Messages:
    308
    Likes Received:
    0
    Location:
    russia
    One hardware issue my intergators met many times: temperature sensor works correctly, but shows temperature (on c-touch) 5-10 degrees higher, than actual is. So when is is 20, it shows 30, which is clearly untrue to any client.

    Anyone same problem?
     
    nickrusanov, Sep 8, 2004
    #1
  2. nickrusanov

    Clyde

    Joined:
    Aug 4, 2004
    Messages:
    33
    Likes Received:
    0
    Location:
    Cumbria, UK
    Yes Nickrusanov,

    We had exactly the same problem with 12 temp sensors linked to a c-touch screen. We had the recorded temp level showing for particular zones on the screen. All showed the wrong temp, according to our client. :( with his mercury thermometer.When we adjusted the target levels for each zone, we removed the temp level from the display.
    A problem I hope the tech guys can help with.
     
    Clyde, Sep 9, 2004
    #2
  3. nickrusanov

    nickrusanov

    Joined:
    Aug 5, 2004
    Messages:
    308
    Likes Received:
    0
    Location:
    russia
    I was sure, I'm not alone

    Did you have any sensor, showing _correct_ temperature?
     
    nickrusanov, Sep 9, 2004
    #3
  4. nickrusanov

    Clyde

    Joined:
    Aug 4, 2004
    Messages:
    33
    Likes Received:
    0
    Location:
    Cumbria, UK
    No unfortunately not, all the temp sensors appeared to be calibrated 3-5 deg C above actual temp. We tried several different test thermometers.
     
    Clyde, Sep 10, 2004
    #4
  5. nickrusanov

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    A bulletin went out about Temperature sensor calibration very early this year.

    If a unit is added to the database and then saved to a unit on the network the factory calibration factor is overwritten.

    The only way to program a Temperature Sensor and maintain the factory calibration factor is to work on the unit live on the network. Never transfer a SENTEMP configuration from the database to the network.

    If the calibration factor becomes overwritten then the unit needs to be returned to the factory for re-calibration.
     
    Newman, Sep 10, 2004
    #5
  6. nickrusanov

    Clyde

    Joined:
    Aug 4, 2004
    Messages:
    33
    Likes Received:
    0
    Location:
    Cumbria, UK
    Hello Newman,
    The temp sensors were fitted Jan 04, and if I remember they were installed one at a time, and the local network uploaded, targets and margins were then adjusted, and then saved to the database as well as the network. Is this 'working the unit live on the network' ?
    We have a few more to fit on other jobs, approx sixteen, complete with c-touch/s. It looks good when the room temp is displayed and we would like to keep this feature.
    Being in the UK we dont seem to get Bulitins, can they be found on-line

    Is there any way the client can adjust the target temp if it has been set to low/high?
    Regards Clyde
     
    Clyde, Sep 13, 2004
    #6
  7. nickrusanov

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Clyde

    The info in Technical bulletins and the like get collated into a newsletter every once in a while when there's sufficient material to put one together. Previous newsletters can be downloaded from here:

    http://www.clipsal.com/cis/lit_installtraining_news.php3

    Unfortuantely the issue with calibration of Temperature Sensors hasn't made it to a newsletter yet :(

    Yep, that's it, you should be OK.

    Nope, can't do that. It's not trivial getting the temperature out of the temperature sensor, let alone re-configure it on the fly.

    The SENTEMP's are fairly sensitive with respects to mounting orientation too. Make sure they're mounted the correct way up on a vertical wall.
     
    Newman, Sep 14, 2004
    #7
  8. nickrusanov

    Clyde

    Joined:
    Aug 4, 2004
    Messages:
    33
    Likes Received:
    0
    Location:
    Cumbria, UK
    Thanks Newman

    not being funny, but why does the orientation make a difference ?
     
    Clyde, Sep 14, 2004
    #8
  9. nickrusanov

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Cyde

    It's all to do with where the heat from the PCB inside the unit goes.

    In a vertical orientation most of the heat from the unit just goes up and out the unit. It doesn't affect the temperature sensor too much. Mount the unit on it's back however and the heat from the pcb rises up past the sensor giving an artificially high reading.

    The heat generated by the PCB isn't much but it's enough to influence the sensor reading by several degrees if mounted the wrong way. This gets worse if the unit is mounted in very still air.
     
    Newman, Sep 14, 2004
    #9
  10. nickrusanov

    Clyde

    Joined:
    Aug 4, 2004
    Messages:
    33
    Likes Received:
    0
    Location:
    Cumbria, UK
    Cheers Newman,
    Last question for tonight, what about ceiling mounting the temp sensors?
     
    Clyde, Sep 14, 2004
    #10
  11. nickrusanov

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Ceiling mount isn't the best idea because of the airflow you can get through the unit. Any air moving from the roof space through the unit and out past the sensor will carry with it heat from the unit PCB.

    Air moving throught the unit and out into the roof space is less of a problem.

    Don't forget a roof mounted temperature sensor will be reading the hottest air in the room, as hot air rises. Take a thermometer and stick it on your ceiling. Take another one and put it on the floor and you will see the temperature difference!
     
    Newman, Sep 14, 2004
    #11
  12. nickrusanov

    Clyde

    Joined:
    Aug 4, 2004
    Messages:
    33
    Likes Received:
    0
    Location:
    Cumbria, UK
    yep sounds logical, thanks for you help Newman

    Regards Clyde
     
    Clyde, Sep 16, 2004
    #12
  13. nickrusanov

    Alex

    Joined:
    Aug 3, 2004
    Messages:
    21
    Likes Received:
    0
    Location:
    Sydney
    In addition to self-heating, the temperature sensors have another basic design flaw, in that there is a pathway for airflow from the wall cavity to/from the room. I have found that this can cause readings that are several degrees above/below room temperature, depending on which way the air is flowing and the temperature of the air in the cavity. The effect is most noticeable with sensors mounted on the inside of exterior walls.

    I have been able to reduce but not eliminate this with a plastic cover mounted behind the sensor (made from the packing material they come in) and jamming insulation behind them.

    I also believe that the sensors need a larger thermal mass in contact with the air. Simply exposing the sensor element to the air as in the current design makes them too sensitive to minor local temperature fluctuations, and contributes to self-heating problems.
     
    Alex, Sep 18, 2004
    #13
  14. nickrusanov

    Clyde

    Joined:
    Aug 4, 2004
    Messages:
    33
    Likes Received:
    0
    Location:
    Cumbria, UK
    I did hear talks of a new temp sensor being designed (just before our installation Jan 04), but I have not heard any thing since. Can any one shed any light as to wether a new temp sensor is in development.(without giving too much away)
     
    Clyde, Sep 18, 2004
    #14
  15. nickrusanov

    nickrusanov

    Joined:
    Aug 5, 2004
    Messages:
    308
    Likes Received:
    0
    Location:
    russia
    agree

    Yes, and Thermostat, which hopefully will work with it.
     
    nickrusanov, Sep 19, 2004
    #15
  16. nickrusanov

    ICS-GS

    Joined:
    Nov 1, 2004
    Messages:
    347
    Likes Received:
    0
    Location:
    SE Melbourne
    New Temp sensors

    If and when thes new sensors are to be released i hope they have the ability to be able to have target temp's set from a c-touch.
    Most of my clients are extremely disappointed with this oversight. :( also the ability to select the heating or cooling functions (or do away with them all togeother).
    We tell them we can control anything they want, and that they have 'full' control over anything in the house, but we must 'set' the temperature there house runs at and leave them with it.... :eek:
     
    ICS-GS, Nov 8, 2004
    #16
  17. nickrusanov

    Sergio

    Joined:
    Apr 18, 2005
    Messages:
    28
    Likes Received:
    0
    Whats wrong?

    We install new Temp Sensor in network with lots other switches and ets, then scan the network, run unravel feature, readress units and save to database.
    Temp Sensor which was found in live network in above process, and saved to database show wrong (high) temperature now.
    Whats wrong we do?
     
    Sergio, Aug 11, 2005
    #17
  18. nickrusanov

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    V2 or Toolkit? V2 had problems overwriting the calibration of Temperature Sensors.
     
    Newman, Aug 12, 2005
    #18
  19. nickrusanov

    Sergio

    Joined:
    Apr 18, 2005
    Messages:
    28
    Likes Received:
    0
    to Newman

    We use toolkit 1.1.7
     
    Sergio, Aug 12, 2005
    #19
Ask a Question

Want to reply to this thread or ask your own question?