Strange behaviour of L5512

Discussion in 'General Discussion' started by 2SC, Jul 28, 2008.

  1. 2SC

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    344
    Likes Received:
    0
    Location:
    Athens, Greece
    In a hotel project there are 3 suites feeded with 3phase power. There is also a stand by generator which takes the loads after some seconds of power cut.

    Can anyone explain why on the 2 of the 3 suites, when the generator start to operate, the 1st channel of a L5512 close its contact without opening the indication light on the relay? As a result a shutter start to operate.

    When someone press the button 2 times the relay start to operate normal again.

    Any ideas?

    PS: I am sorry for my difficulty to express myself in English
     
    2SC, Jul 28, 2008
    #1
  2. 2SC

    zip_cool

    Joined:
    Sep 14, 2006
    Messages:
    80
    Likes Received:
    0
    yeah, same like what i occur here, but the different is we connect to a light.. is that because of the issued of the frequently of generator???
     
    zip_cool, Aug 8, 2008
    #2
  3. 2SC

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    344
    Likes Received:
    0
    Location:
    Athens, Greece
    Propably this is the reason Technical support said.
    I will put a network burden and if the problem remain I will put a shutter relay...
     
    2SC, Aug 8, 2008
    #3
  4. 2SC

    Darpa

    Joined:
    Apr 30, 2006
    Messages:
    426
    Likes Received:
    0
    Location:
    Australia
    You could install a power conditioner unit or a true sinewave UPS between the generator and the CBus units. This would solve your problem if that problem is caused by the frequency or voltage of the generator's output.
     
    Darpa, Aug 9, 2008
    #4