Shutter relay - multiple motors

Discussion in 'C-Bus Wired Hardware' started by Moricild, Oct 14, 2010.

  1. Moricild

    Moricild

    Joined:
    Aug 12, 2010
    Messages:
    6
    Likes Received:
    0
    Location:
    Melb
    Hi

    Assuming that I want to open/close windows only together with one another, is it possible to run more than one motorized window winder from the same c-bus shutter relay provided, of course, that the total load remains under 2A?

    Thanks

    M
     
    Moricild, Oct 14, 2010
    #1
  2. Moricild

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Connecting multiple motors together off a single relay is not a good idea. Relay contact life would be shortened significantly under these circumstances, although how much the life will be reduced varies with the exact type and construction of the motors used.
     
    Newman, Oct 14, 2010
    #2
  3. Moricild

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    most motor makers discourage this also.
     
    Charlie Crackle, Oct 14, 2010
    #3
  4. Moricild

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    There are some non C-Bus controllers that do allow multiple motors to be connected, but they have seperate terminals for each montor - there is no parallel wiring involved. These can then be connected to a C-Bus relay for integration into the C-Bus system. I have one running two roller shutters in unison.

    You should be able to use two controllers and have use the same group names, that way the appear to be one and whenever one goes up so will the other.

    Mick
     
    znelbok, Oct 14, 2010
    #4
  5. Moricild

    conor1

    Joined:
    Feb 13, 2007
    Messages:
    135
    Likes Received:
    0
    Location:
    Northern Ireland
    Multiple motors

    Hi ,
    I have 3 230v vertical blinds running off 1 shutter relay all in one room aprox 300mm apart ,generally they work fine but occasionally one won't open , this is generally when wife only touches Saturn quickly but if you hold it longer never a problem .
    Regards conor
     
    conor1, Oct 14, 2010
    #5
  6. Moricild

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Make sure that the FailSafe time in all shutter relays sharing the same group is identical, otherwise you might get some strange behaviour as one unit thinks the blinds are closed when another thinks they are open.
     
    Newman, Oct 15, 2010
    #6
  7. Moricild

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    It will work, just don't expect the Shutter Relay unit to last a long time in this configuration. You'll also probably struggle to get a successful warranty claim out of either Clipsal or the motor manufacturer if anything fails.
     
    Newman, Oct 15, 2010
    #7
  8. Moricild

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,420
    Likes Received:
    62
    Location:
    Adelaide
    Don't Do This!

    The shutter relay is designed to run a single motor. Do not wire multiple motors in parallel to a single shutter relay.

    The motor manufacturers' instructions I have seen specifically prohibit wiring multiple motors in parallel to a single switching device... one of the reasons is that you can get feedback through the internal limit switches and other circuit elements in the motor which can result in oscillation... I know this can destroy relays quickly, and I suspect it would make short work of the motor's limit switches and/or gearbox.

    If you really need to run multiple motors off a single shutter relay, you could fit external relays (two for each motor - one for up and one for down), and drive the coils of these from the shutter relay. By the time you've done this though it's probably easier/cheaper to just use a shutter relay per blind.

    Nick
     
    NickD, Oct 15, 2010
    #8