Send command directly to Wiser 2 CNI

Discussion in 'C-Bus Wiser 2 Controller' started by mcsortan, May 31, 2019.

  1. mcsortan

    mcsortan

    Joined:
    Mar 16, 2013
    Messages:
    36
    Likes Received:
    0
    Location:
    adelaide
    Is it possible to send a command directly to the Wiser 2 CNI via its' fixed IP address and port 10001.
    I'm setting up Cbus control in Demopad and having a few problems.
    For example

    Group 16 ON
    \5380079103Ag

    thanks
     
    mcsortan, May 31, 2019
    #1
    1. Advertisements

  2. mcsortan

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,371
    Likes Received:
    32
    Location:
    Adelaide
    Yes, it is possible... as long as nothing else is already connected (it only accepts one connection at a time).

    You are missing the leading 0 though..

    \0538007910

    The 3A is the checksum which may or may not be necessary depending on the mode of the PCI (which you should initialise when you connect). The g is a confirmation character which you can omit if you don't intend to check the result returned.

    Nick
     
    NickD, May 31, 2019