scene from PAC randomly missing commands

Discussion in 'C-Bus Wired Hardware' started by Rod, Sep 29, 2022.

  1. Rod

    Rod

    Joined:
    May 24, 2022
    Messages:
    5
    Likes Received:
    0
    I have a pac with a small welcome scene approx. 30 groups triggered from a wall switch.
    It doesn't consistently work some days it is fine other days a few lights do not turn on that should.
    Any ideas
     
    Rod, Sep 29, 2022
    #1
  2. Rod

    xrmichael

    Joined:
    Nov 20, 2006
    Messages:
    113
    Likes Received:
    1
    Location:
    uk
    Are they not being sent or not being received have you checked in the toolkit log ?. I have seen PACs reset if they get overworked you could set a flag to test for this.
     
    xrmichael, Sep 30, 2022
    #2
  3. Rod

    Rod

    Joined:
    May 24, 2022
    Messages:
    5
    Likes Received:
    0
    Missing commands are not being sent by PAC. Can you explain setting a flag
     
    Rod, Sep 30, 2022
    #3
  4. Rod

    xrmichael

    Joined:
    Nov 20, 2006
    Messages:
    113
    Likes Received:
    1
    Location:
    uk
    Put something in the PAC 'logic initialization' to turn on a unused lighting group, reboot the PAC this group should turn on, then manually turn it off. If it comes back on the PAC has reset.

    I had issues with a large all off scene (would reboot the PAC) it had to be broken up into smaller room off scenes and triggered with some delay between them.
     
    xrmichael, Oct 1, 2022
    #4