Problems with scheduler

Discussion in 'General Discussion' started by Mickylou, Jun 7, 2019.

  1. Mickylou

    Mickylou

    Joined:
    Jun 7, 2019
    Messages:
    2
    Likes Received:
    0
    Hi very new to Cbus it is in my building and we are recently having a few problems with scheduling

    We have male and female lights on the same circuit breaker. They are both set to come on at 8am and turn off at 6pm . The male toilets lights always trigger. The female trigger to come on half the time. If I reset the circuit breaker they both come back on.

    Can anyone shed some light?

    Thanks
    Katrina
     
    Mickylou, Jun 7, 2019
    #1
  2. Mickylou

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,420
    Likes Received:
    62
    Location:
    Adelaide
    It could be many things.. The fact that it half works suggests something on the load side... my guess is the lights are DALI and the C-Bus DALI gateway side does not have status correction enabled. This could be an oversight or it could be intentional depending on the rest of the system design.

    Does the circuit breaker you are resetting switch power to just the lights or does it reset the whole of C-Bus?

    Nick
     
    NickD, Jun 7, 2019
    #2
  3. Mickylou

    Mickylou

    Joined:
    Jun 7, 2019
    Messages:
    2
    Likes Received:
    0
    The circuit break is just for those 2 sets of light not all of CBus.
     