Problem with Cbus not responding immediately

Discussion in 'C-Touch/HomeGate/SchedulePlus/PICED Software' started by loesch, Mar 9, 2010.

  1. loesch

    loesch

    Joined:
    Mar 9, 2010
    Messages:
    11
    Likes Received:
    0
    Location:
    somerset west
    I bought home with HomeGate 3.4.1.0 CGate 2.5.23 build 2123,

    The computor does not respond when I click the icons on the screen ,the functions then only come on after I clicked on the time of the computor at the bottom right and ok .
    What can be the cause ,and can I download a newer better version , everything was working fine but computor was not responding and had to be switched of ,problem started after this problem .It show 0/1 networks online and only change for a short time to 1/1 network online if I click on the time or go to operation mode .I tried to reinstall HomeGate 3.4.1.0 but it gives the following error 1,setup has failed to find a valid install of homegate
    please help urgently:confused:
     
    Last edited by a moderator: Mar 9, 2010
    loesch, Mar 9, 2010
    #1
  2. loesch

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    It sounds like the PC might have a few issues going on there, so the best place to start is with a phone call to Clipsal Technical Support.

    http://www2.clipsal.com/cis/technical/technical_support

    Some useful information to gather before you call will be things like:

    • Tech specs of the PC it's installed on
    • Whether you are using a touchscreen or a mouse for input
    • Operating system the PC is running on
    • Whether the HomeGate dongle is plugged into the PC (without the dongle, HomeGate will not operate correctly as it tells HomeGate that it is a legal copy of HomeGate)
     
    Newman, Mar 9, 2010
    #2
  3. loesch

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    If it shows 0/1 networks on-line, then there are communications problems. HomeGate can not control C-Bus if the networks are off-line. You need to solve this problem before doing anything else. Refer to the document C:\Clipsal\HomeGate\Manuals\Advanced Fault Diagnosis.pdf for details of analysing site problems.

    Do you have the CD with HomeGate on it?

    If not, it is possible that your version of HomeGate is not licensed.

    From a valid version 3.4.1 of HomeGate, you should be able to upgrade to V3.9.0 to get a more up to date version. This can be obtained by going to http://www2.clipsal.com/cis/technical/downloads/home_gate and clicking on the Show Old Versions link. To go past this version, you will need to purchase a dongle.
     
    Darren, Mar 9, 2010
    #3
  4. loesch

    loesch

    Joined:
    Mar 9, 2010
    Messages:
    11
    Likes Received:
    0
    Location:
    somerset west
    Problem with connecting to c bus

    Thank you for the help I downloaded the homegate 3.9 and cbus toolkit 6.1 ,and it works fine now on start up for 5 minutes it showns 1/1 network online ,and after 10minutes 0/1 network online .
    In the jave screen it shows: Hardware key initialize failed(driver not installed)
    license file found: customer name :public,location:public , license type:public,network license:2, expiry: 31 december 2099 and then
    20100311-133524 827 //d_cook/254 4f22b760-6e3a-1028-92cb-e9897d67db5b c-bus send error: (%) (retrying)
    checking license

    please help
     
    Last edited by a moderator: Mar 11, 2010
    loesch, Mar 11, 2010
    #4
  5. loesch

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Prior to V4 of HomeGate, it was C-Gate that had to be licensed. Since V4, it is HomeGate that needs the license.

    So for V3.9 of HomeGate, you will need to have a C-Gate dongle. If you don't have one, C-Gate will time-out.
     
    Darren, Mar 13, 2010
    #5
  6. loesch

    loesch

    Joined:
    Mar 9, 2010
    Messages:
    11
    Likes Received:
    0
    Location:
    somerset west
    C bus License and homegate

    Thank you ,I have a clipsal pc interface RS232 connected to the serial port.Which version do I need to install just to get everything working,because everything was working fine before the power out.After I installed the newer versions the one black and white keypad started rebooting every minute.I had the homegate 3.4.1 originally installed ,which cgate and cbus toolkit need I install to get everything just to work.pleaseeeeee

    Regards
    Loesch
     
    loesch, Mar 15, 2010
    #6
  7. loesch

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The C-Bus software downloads pages show a compatibility chart to show which versions of the various pieces of software work with each other.
    http://www2.clipsal.com/cis/technical/downloads/home_gate

    If possible, I would try and persevere with HomeGate 3.9.0. It will enable you to use newer versions of the other C-Bus software products, which might not be so important now, but could become an issue if you decide to expand on your installation with products that weren't available at the time those old software versions were created.

    You say:
    ... can you give some more information? Is this a C-Bus product? How is it related to your HomeGate installation?
     
    Newman, Mar 15, 2010
    #7
  8. loesch

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    You haven't said whether there is a dongle plugged into your PC. This determines what is possible.
     
    Darren, Mar 15, 2010
    #8
  9. loesch

    loesch

    Joined:
    Mar 9, 2010
    Messages:
    11
    Likes Received:
    0
    Location:
    somerset west
    homegate not working

    Thank you ,I have a clipsal pc interface RS232 connected to the serial port,is that what you are talking about.

    which version should I download of homegate and cbus in the meantime ,and where can I get a dongle and will it sort out all the problems.

    regards
    Loesch
     
    loesch, Mar 16, 2010
    #9
  10. loesch

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The Clipsal PC Interface is not the dongle, it is just the interface between the PC and the C-Bus network.

    A C-Gate dongle is a parallel port adapter that plugs into the parallel port of your PC. When you buy HomeGate (it is not free) the licence is supplied on this parallel port adapter, called a dongle.

    If you have bought this house recently, but the owner has not left you the parallel port dongle on the PC running HomeGate, then he has effectively taken your permission to use HomeGate with him.
     
    Newman, Mar 16, 2010
    #10
  11. loesch

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    It has been a very long time since we have worked with HomeGate V3.9 and the associated C-Gate. I think that we may have provided some misleading information.

    For this version of software, you did need a dongle for C-Gate, but only if you had more than 2 C-Bus networks. The dongle is the device which plugged into the PC parallel port as Newman said.

    If you only have 1 or 2 C-Bus networks, C-Gate should run OK.

    So the question remains about why the C-Bus networks are going off-line. The only way to know for sure is to obtain a C-Gate "event level 9 log". To do this:
    1. Close HomeGate and C-Gate
    2. Open the C-Gate configuration file (c:\Clipsal\C-Gate2\C-GateConfig.txt)
    3. Activate logging by setting use-event-file to yes
    4. Select the log file name using the event-filename parameter
    5. Select the level of event reporting using the global-event-level parameter. Event level 5 is the normal setting. Event level 9 records everything. Set to level 9 for now.
    6. Save the file when complete
    7. Start HomeGate and wait until you see the networks go into the error state.
    8. Close HomeGate and C-Gate
    9. Send the log file to CIS technical Support and ask them to forward it to me
    10. Disable the C-Gate log again (similar to steps 2 to 6, but set use-event-file to no)
     
    Darren, Mar 16, 2010
    #11
  12. loesch

    daniel C-Busser Moderator

    Joined:
    Jul 26, 2004
    Messages:
    769
    Likes Received:
    21
    Location:
    Adelaide
    daniel, Mar 17, 2010
    #12
  13. loesch

    loesch

    Joined:
    Mar 9, 2010
    Messages:
    11
    Likes Received:
    0
    Location:
    somerset west
    Problem black/white touch screen model 5000ct

    Thank you very much for feedback ,getting there slowly.
    When connecting from computor through Piced the following error 14023 could not connect to serial port.Unable to open comport (win error code 5).
    Where must I do what ?pleaseeeee
     
    loesch, Mar 22, 2010
    #13
  14. loesch

    loesch

    Joined:
    Mar 9, 2010
    Messages:
    11
    Likes Received:
    0
    Location:
    somerset west
    Problem black/white touch screen rebooting every 10 seconds model 5000ct

    Thank you for the help,slowly getting there.
    Following error when connecting with Piced 3.9 to the touch screen.
    error 14603 could not connect to unit ,communications failed.
    The touch screen keeps rebooting every 10 seconds:( .Pleaseeee help
     
    loesch, Mar 22, 2010
    #14
  15. loesch

    loesch

    Joined:
    Mar 9, 2010
    Messages:
    11
    Likes Received:
    0
    Location:
    somerset west
    error message in java when homegate opens

    Thank you Darren for all the help
    date -time //dcook/254/ 4f22b760-6e3a-1028-92cb-e9897db5b C-Bus Send error: retrying
    unit sync failed
    and then checking license
    but license is shown as expiry 31 dec 2099
    c gate v2.5.23 and homegate 3.4.1

    please help
     
    Last edited by a moderator: Mar 24, 2010
    loesch, Mar 23, 2010
    #15
  16. loesch

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Which version of firmware do you have in the touch screen?
     
    Darren, Mar 24, 2010
    #16
  17. loesch

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    We will need an extract from a C-Gate event level 9 log at the time of this unit sync failure to determine what is going on.
     
    Darren, Mar 24, 2010
    #17
  18. loesch

    loesch

    Joined:
    Mar 9, 2010
    Messages:
    11
    Likes Received:
    0
    Location:
    somerset west
    touch screen problem

    C Touch Firmware : 2.22.0
    C Bus Firmware :4.4.00

    the other touch screen is working fine
     
    Last edited by a moderator: Mar 24, 2010
    loesch, Mar 24, 2010
    #18
  19. loesch

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    This is a very old version of firmware. There is currently a problem with C-Touch re-booting (which will be fixed in a service pack very soon), but this is a very recent issue. Firmware V2.22.0 would not have this problem.

    It is difficult to know what the problem might be with this unit.

    The new version of PICED about to be released will have a new feature which might be able to stop the unit from resetting so that you can re-program it.
     
    Darren, Mar 25, 2010
    #19
  20. loesch

    loesch

    Joined:
    Mar 9, 2010
    Messages:
    11
    Likes Received:
    0
    Location:
    somerset west
    C touch screen

    Thanx when and where can i download it.
    Regards
     
    loesch, Mar 25, 2010
    #20