Problem with 5031NMML?

Discussion in 'C-Bus Wired Hardware' started by grw001, Jan 29, 2018.

  1. grw001

    grw001

    Joined:
    Dec 6, 2010
    Messages:
    8
    Likes Received:
    0
    Location:
    Sydney
    Hi there

    I have four 5031NMML and slave switches each programmed to control fans with lights in four bedrooms. The lights are wired into universal dimmer units (L5504D2U) and the fans to sweep fan controllers (L5501RFCP) Three of the 5031NMMLs work perfectly.

    The fourth has been turning on/off other lights when the button programmed to turn on the fan is pressed. Using the Control Systems IP Utility, when I press the switch to turn on the fan, the switch appears to be sending out the following commands: turn one light to 1% (GA 68 which is the light in the fan/light), three other lights off (GA 32, 38 and 14 which have no relationship with this fan/light) and one other light to 4% (GA 5 which also has no relationship to the fan/light). The behaviour is entirely repeatable.

    I have carefully checked the programming/configuration for this switch and it is identical (other than the devices it is programmed to control) from the three working 5031NMML. No where in the configuration of this switch does the programming mention GA 32, 38, 14 or 5).

    I have checked the physical wiring of the switch and it looks fine. I plan to do a factory reset and reprogram it.

    But I was wondering if I possibly have a hardware problem with the switch? Could it be sending out spurious c-bus commands?

    Thanks for any advice
    Glenn
     
    grw001, Jan 29, 2018
    #1
  2. grw001

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,420
    Likes Received:
    62
    Location:
    Adelaide
    You refer to the IP utility but I don't think this does what you describe... do you mean the Diagnostic Utility?

    Can you post a log from the Diagnostic utility that shows the commands that result when you press the problem button?

    Nick
     
    NickD, Jan 30, 2018
    #2
  3. grw001

    grw001

    Joined:
    Dec 6, 2010
    Messages:
    8
    Likes Received:
    0
    Location:
    Sydney
    Nick ... yes I meant the Diagnostic Utility. I'll post the output from that when I get home this evening.
     
    grw001, Jan 30, 2018
    #3
  4. grw001

    grw001

    Joined:
    Dec 6, 2010
    Messages:
    8
    Likes Received:
    0
    Location:
    Sydney
    Hi Nick

    Here is the output from the diagnostic utility highlighting the relevant lines:

    22:06:33 Rx : = Local Network, Source Unit 21, Measurement, Measurement: Device 254 Channel 0 = 0 Litres
    22:06:33 Rx : 0579CA00020300B3<CR> "_y______"
    22:06:33 Rx : = Local Network, Source Unit 121, Trigger Control, Ctrl: Grp 3 set to 0
    22:06:33 Rx : 0579380002440101200124010E02050A9D<CR> "_y8__D__ _$______"
    22:06:33 Rx : = Local Network, Source Unit 121, Lighting, GA 68 Set to 1; GA 32 Off; GA 36 Off; GA 14 Off; GA 5 Set to 4%
    22:06:33 Rx : 05793800011633<CR> "_y8___3"

    22:06:33 Rx : = Local Network, Source Unit 121, Lighting, GA 22 Off
    22:06:33 Rx : 05123800024A0065<CR> "__8__J_e"
    22:06:33 Rx : = Local Network, Source Unit 18, Lighting, GA 74 Set to 0%
    22:06:33 Rx : 0512CA00A7030100014F666658<CR> "_________OffX"
    22:06:33 Rx : = Local Network, Source Unit 18, Trigger Control, Ctrl: Grp 3 Label, Variant 0, Language 1 [English], Action Selector 0, Text label, 3 Bytes = "Off"
    22:06:33 Rx : 0512CA00090313<CR> "_______"
    22:06:33 Rx : = Local Network, Source Unit 18, Trigger Control, Ctrl: Grp 3 Scene Indicator Kill
    22:06:36 Rx : 05793800014405<CR> "_y8__D_"
    22:06:36 Rx : = Local Network, Source Unit 121, Lighting, GA 68 Off
    22:06:39 Rx : 0579380079448D<CR> "_y8_yD_"
    22:06:39 Rx : = Local Network, Source Unit 121, Lighting, GA 68 On
    22:06:41 Rx : 05793800014405<CR> "_y8__D_"
    22:06:41 Rx : = Local Network, Source Unit 121, Lighting, GA 68 Off

    Thanks again for any assistance.

    Glenn
     
    grw001, Jan 30, 2018
    #4
  5. grw001

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,420
    Likes Received:
    62
    Location:
    Adelaide
    It looks like unit 121 is the 5031NMML, and unit 18 is the Fan Controller, and the Fan controller is using group 74.

    It also looks like you might have a scene hiding in unit 121 which is being triggered by the same trigger group assigned to the fan controller key.

    I assume the other events from unit 121 (turning group 68 off/on/off) were you pressing a different key?

    Nick
     
    NickD, Jan 31, 2018