Problem in 5753L PIR C bus sensor

Discussion in 'General Discussion' started by samala, Mar 13, 2011.

  1. samala

    samala

    Joined:
    Sep 15, 2008
    Messages:
    11
    Likes Received:
    0
    Hi everybody,

    I am getting a problem at one of the site,Where i have installed cbus 5753L sensor.

    I have programmed the sensors to be enabled at 6PM every day evening.

    The sensors are getting enabled and triggering the lights programmed but the problem is lights are not going off at all.Time delay i have used is 5 mins to switch off the lights.

    But the lights are not going off at all.They are on continuously.

    Can anybody plz help me on this.

    Thanks in advance for immediate reply.
     
    samala, Mar 13, 2011
    #1
  2. samala

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Are you using the same group address to enable the sensor AND control the lights, or are they 2 separate group addresses?

    When you enable the sensors, do they turn on straight away or do they need to wait until someone walks past the sensor?

    What is the timer expiry function for your groups? Is it Off or something else?

    Are the sensors located near air conditioning vents? The draft from these can cause sensors to re-trigger regularly.
     
    Newman, Mar 14, 2011
    #2