I don't know how familiar you are with CBus so I will just mention some basics. Software burden needs to be enabled on unit address 01 which according to your pictures is USB PCI. I don't think that is your problem. If you were having trouble scanning the network and all the unit LED's were normal then that would be something to look at. As far as I can tell when you disconnect part of the network it is taking out the CBus indicator? Keep in mind if you split the CBus network and remove all the clocks the perfectly healthy unit's CBus LED will go out. One clock minimum three recommended for redundancy. Since the network is down you can't scan it to see a list of all the clocks so you need to note all that down from all the output units in the database or whatever scans you were able to do. I think the problem is going to be a faulty unit or a short in the pink cable. Of course knowing the wiring route would be handy at this stage. Split the CBus network up and you will be able to narrow it down. If there is just one distribution board you could disconnect any CBus pink cable going out from there and give that a go for a start.