Philips LED oyster fitting flashing when off

Discussion in 'C-Bus Wired Hardware' started by DarylMc, Jul 8, 2014.

  1. DarylMc

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Hello everyone.
    Not CBus related but I am having some trouble with a Philips LED oyster fitting.
    http://www.simply-leds.com.au/phili...iling-17w-led-luminaire-350mm-warm-white.html

    The light is switched by a 30 series mech and there is no dimmer.
    I have replaced the fitting and checked the switch and wiring insulation resistance but it is still flashing according to the customer.
    Faintly about once per second when switched off.

    I tested the suspect fitting in my office and cannot notice any flashing in the off state so I suspect the problem is some induced voltage in the cable to the light.
    The cable to the light is well clear of other cabling and only parallel to live power running down to the switch.
    Perhaps it could also be leakage across the switch mechanism but my megger says no.

    I believe the property may have some electromagnetic rodent repellent devices.

    I had in mind to test the Clipsal 31LCDA to see if it would help.
    Has anyone seen this before or have any other suggestions.

    Thanks
    Daryl
     
    Last edited by a moderator: Jul 8, 2014
    DarylMc, Jul 8, 2014
    #1
  2. DarylMc

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    I just tested the same light fitting connected to a CBus leading edge dimmer expecting to see it flash or glow in the off state but is does not.
    This suggests to me that it is not terribly susceptible to stray voltages and I am now even more perplexed.
     
    DarylMc, Jul 8, 2014
    #2
  3. DarylMc

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    After some more testing I found that this LED light fitting will illuminate dimly with only an active and earth connected.
    Therefore if it was connected with incorrect polarity it would glow when switched off.

    So now I am off the find out why and how much potential between the neutral and earth in this installation.
     
    DarylMc, Jul 9, 2014
    #3
  4. DarylMc

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,392
    Likes Received:
    24
    Location:
    Adelaide, South Australia
    If it glows with only active and earth connected, then it has some kind of internal ELECTRONIC path from active to earth (kinda obviously).

    Which is strange, perplexing, and possibly no compliant with safety and electrical standards.

    Be careful.
     
    ashleigh, Jul 10, 2014
    #4
  5. DarylMc

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Hi Ashleigh
    Thanks for the feedback

    I tested 3 of these fittings and they all glow with only active and earth connected.
    The glow is so dim you have to be in darkness to see it.
    Probably just a tiny amount of leakage.

    I tried 31LCDA across the lamp with neutral disconnected and it still glows.

    Insulation resistance to earth is infinity.

    Not much more I can do until I can test the installation but I can't get access until next week.
     
    Last edited by a moderator: Jul 10, 2014
    DarylMc, Jul 10, 2014
    #5
  6. DarylMc

    chromus

    Joined:
    Jan 27, 2014
    Messages:
    422
    Likes Received:
    50
    Location:
    Perth
    I have a random issue with some LED drivers, I believe it is as a result of 240V always being there on a dimmer channel, but current is negligible, and for normal (Tube/Filament) lights there is enough internal resistance to collapse the circuit.

    However when it comes to some LED drivers the current draw of the components isn't enough to collapse the circuit so you get flicks occasionally, when "off".

    If I have 2 on a channel, no issues, presumably the load is enough.
     
    chromus, Jul 10, 2014
    #6
  7. DarylMc

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Hi Chromus
    Thanks for the suggestion.
    Yeah I can understand that problem but this is a bit different.
    CBus dimmers have voltage at the output even when off.

    The light fittings in question don't have a problem with that and I deliberately tested them on a CBus dimmer output to evaluate.
    The customer's site has conventional wiring with 30 series switch mechs.
    Switched active power is disconnected and I have tested that.

    I have tested a couple of the Philips LED oyster fittings on a CBus dimmer and they are not giving any trouble even though the dimmer is providing a voltage in the off state to active and neutral terminals.

    The Philips LED oysters in question do display an unusual property of illuminating when there is a potential between neutral (or un switched load conductor) and earth.

    When there is any load on a circuit there will be voltage drop in the cables and a potential difference between earth and neutral.

    I'm sure most electricians will be familiar with shorting a neutral and earth and tripping an RCD or sometimes not if there is no load.
    So some potential difference will often exist between neutral and earth.

    In this case I'm sure the potential difference between neutral and earth is causing the light to flash.
    I've yet to determine whether it is caused by a wiring fault or stray voltages in the neutral or earth due to interference.

    Bad feature Philips Lighting.
    I will certainly be letting everyone know the outcome because if a light is flashing or glowing with the active positively switched off, the first thing anyone would look for is an active to switch wire fault.
    Not a neutral to earth fault.

    What I have yet to test is whether the potential difference between neutral and earth in the installation is due to a wiring fault or some induced voltage.
    The fittings are certainly behaving correctly at my workshop during testing.
     
    Last edited by a moderator: Jul 10, 2014
    DarylMc, Jul 10, 2014
    #7
  8. DarylMc

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,392
    Likes Received:
    24
    Location:
    Adelaide, South Australia
    I have some CFLs, on plain mains ccts, which flick on.

    You can only see this by standing under it in the middle of the night.

    It's cause is capacitive coupling in the mains wiring. This charges the input circuit of the CFL and when there is enough built up charge it tries to strike the lamp. Of course at that point the charge is all consumed and the lamp goes out.

    This is more common on 2 way switching circuits due to longer wire runs / parallel wiring in the same cable.

    There's not a lot you can do about it.

    HOWEVER, in this case its not the same thing, as you have tested it and shown operation when you poke mains into Active and connect earth. Thats a strange and rather odd design.
     
    ashleigh, Jul 11, 2014
    #8
  9. DarylMc

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    The voltage potential in this installation between neutral and earth was due to a fault with the earthing system.
    The flashing in the off state has stopped once that was rectified.
     
    Last edited by a moderator: Jul 17, 2014
    DarylMc, Jul 16, 2014
    #9
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.