PEIRL Pulsing Group for Light Control - Override Problem

Discussion in 'General Discussion' started by Guff, Oct 27, 2008.

  1. Guff

    Guff

    Joined:
    Feb 6, 2008
    Messages:
    31
    Likes Received:
    0
    Hi All,

    I want to post this query as I'm not entirely sure how to tackle the best solution for this project.

    Consider an internal powder room (no windows as it is in the middle of the house) with a Multisensor PEIRL installed. The sensor target light is set to max, and is used to turn lights on automatically and turn off after 15min of inactivity.

    The way the PEIRL has been setup is that it pulses a group "powder room sensor" for 1 second. A PAC then turns on the lights and starts a timer, lights are either turned on full, or to a variable defined level during the night (so someone going to toilet at night doesn't get blinded). The fan is turned on after a predetermined time also in case the "user" forgets :p .

    Problem occurs when the person leaving the powder room turns off the lights - they "usually" turn right back on, then the person has to turn the light off again (always turns off then). We've setup the PAC logic so that once powder room goes off, then the powder room disable is pulsed on for 10 seconds.

    I assume that the PEIRL is activating whilst the person is exiting the room, and so even when the light is turned off, the one second pulse given to "powder room sensor" is enough to get it ove the delay of the PAC disabling the sensor for 10 seconds.

    Has Any one tackled this better than I? Many thanks in advance!

    code:

    once ((GetLightingState("Powder Room") = OFF ) and (TimerTime(PowderRmTimer) <> -1)) then
    begin
    TimerStop(PowderRmTimer);
    SetLightingState("Powder Room Sensor", OFF);
    PulseCBusLevel("Local Network", "Lighting", "Powder Room Sensor Disable", 100%, "0s", "0:00:10", 0%);
    end;

    once (GetLightingState("Powder Room Sensor") = ON ) then
    begin
    SetLightingLevel("Powder Room", GetLightingLevel("Night Light Level"), "1s");
    TimerStart(PowderRmTimer);
    end;

    once TimerTime(PowderRmTimer) >= "0:15:00" then
    begin
    TimerStop(PowderRmTimer);
    SetLightingLevel("Powder Room", 0%, "5s");
    end;
     
    Guff, Oct 27, 2008
    #1
  2. Guff

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    There's a couple of different things you could do. I'm sure others will think of more ways to solve this problem.
    • You could configure the button that the user is pressing to turn the lights off as a timer, say with a 2 or 3 second expiry, just long enough for them to get out the door.
    • You could configure the button that the user is pressing to turn off both the lighting Group Address AND a second Group Address that disables the sensor. The PAC could then re-enable the sensor a few seconds later, by which time the person has left the room.
     
    Newman, Oct 27, 2008
    #2
  3. Guff

    ICS-GS

    Joined:
    Nov 1, 2004
    Messages:
    347
    Likes Received:
    0
    Location:
    SE Melbourne
    or just get rid of the key input unit:p
     