Object Log help

Discussion in 'C-Bus Automation Controllers' started by Nobes, Nov 16, 2017.

  1. Nobes

    Nobes

    Joined:
    Oct 7, 2004
    Messages:
    164
    Likes Received:
    1
    Location:
    Hobart
    Hi Guys,

    Need a bit of help with a group turning on during the night. Happens about once every 4 weeks roughly
    As you will see, the bath fan turns on at 4:55am, I presume object means unit 50 instigated it?
    The decoded value is strange. 72>73 (20s), 60>73 (20s), 48>73 (20s).
    Then what's the object data?

    Cheers,

    Chris.
     

    Attached Files:

    Nobes, Nov 16, 2017
    #1
  2. Nobes

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,524
    Likes Received:
    173
    Location:
    Adelaide, Australia
    The object is the group address (i.e. LwrBathFan), not the initiating unit. IThe data gives to the start value, end value and ramp time. I don't know any way of getting the initiating unit from the Automation Controller. Best bet is to run the Cbus diagnostic routine for a while and add a filter for that ga. It will tell you the initiating unit. You could also use toolkit to find all units containing a reference to group 50.
     
    Ashley, Nov 16, 2017
    #2
  3. Nobes

    Nobes

    Joined:
    Oct 7, 2004
    Messages:
    164
    Likes Received:
    1
    Location:
    Hobart
    Hi Ashley,

    Thanks, might be nice for a firmware update to include initiating address in log :)

    Hard to track when it only happens every 4 or so weeks...
     
    Nobes, Nov 17, 2017
    #3
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.