Hi guys I'm hoping someone can help confirm what's going on with my C-Bus install - I suspect it is a dead 12-channel relay, but happy to be convinced otherwise! My C-Bus system was installed about 3 years ago. Layout is a main distribution board at the front of the house, and a sub-board on each of the three levels. Each board has 1, 2 or 3 C-Bus output units installed. The C-Bus data cable is a star topology from the main board to the sub-boards, and then daisy-chained from each sub-board to all the switches on that level. My electrician did all the cabling/install, I supplied the C-Bus hardware and did the programming. This setup has been working perfectly fine up until a few weeks ago, until the following symptoms appeared: [LIST] [*]Some lights on the first floor would occasionally flicker or go out, only to come back on anywhere from a few seconds to a few minutes later. The LEDs on the relevant switches stayed lit when this happened. This happened very occasionally, but increased in occurrence to perhaps once every few days. The affected lights were on an 8-channel dimmer, not the 12-channel relay (These are the only two output units on the first floor). [*]I then started noticing that lights would be off, but the LED indicator on the switch would be lit, ie I'd go downstairs leaving lights on upstairs, then when I went back up later, the switch plate would be lit but the lights out. Pressing the switch off then on again would turn the light back on. This became a multiple times per day occurrence, but only affecting the first floor. At this point, I was thinking there was an issue with the 8-channel dimmer. [*]About a week ago, all the output units in the house stopped responding one night. Lights that were off could not be turned on and vice versa. The local override buttons on the 1st floor and ground floor output units weren't responding. About 15 minutes later, I went to the main board near the front door, and tried the single 5504RVF and it worked. All the lights in the house at that point started working normally again. [*]Late last week, some of the LEDs on the first floor switches started flickering intermittently. Around this point, the 12-channel relay, which looked like it had been behaving up to this point, just stopped working. Three lights were on from this unit and could not be turned off by the relevant switches, nor the local override buttons. Neither could I turn on any other lights from this relay. Both the unit light and the C-Bus light on this unit are out, but the 3 local override buttons remain on (see photo attached). None of the local override buttons work. I've tried flicking the breaker for this unit, but when I turn it back on, it remains in its unresponsive state. Because one of the lights stuck on is my bedside lamp, I've had this unit turned off at the breaker for the past few days. [*]Since then, the rest of the lights upstairs (on the 8-channel dimmer) seem a little more stable. I still have had occurrences of lights turning themselves off, but it's not as frequent. Like before, I sometimes can't turn them back on for a few minutes. The fact that it is still occurring though bothers me, and is making me wonder if there is a network issue, or if the dimmer is on the way out too. [/LIST] [ATTACH]2327[/ATTACH] Some further information that may be helpful: [LIST] [*]There are 34 units on the network. [*]I have three clocks enabled, one on a unit in each sub-board. The relay in question does not have the clock enabled, but the dimmer mentioned does. [*]I have one hardware burden, installed in my PACA (also used as a PC interface when I fire up toolkit), located in the basement. [*]According to toolkit, current consumption is 524mA with a supply current of 1600mA. Impedance is 406 ohms. [*]Power supplies are well distributed (all embedded in output units). When I run the diagnostics, unit voltage is pretty constant across the whole network, with a low of 30.2V and a high of 31.6V. [*]All C-Bus units were bought new, except the 12-channel dimmer and 8-channel relay used on the first floor, can't remember the manufacturing date of these two units (when was green a C-Bus colour?!), but they are probably 8-9 years old. Was a bit short on cash at the time...might be paying for it now though! [*]The only logic in the PACA is a schedule for turning on 4 or 5 lights at sunset, and then back off again around midnight. Two of these lights are running from the dimmer on the first floor. [*]I've checked for loose connections in the relay, all good. [*]In the first floor sub-board, the C-Bus cable from the main board goes into the 12-channel relay, then to the 8-channel dimmer, then to all the first floor switches. Even with the relay powered down, the network still works and scans fine, presumably because the two RJ45s in the unit are physically connected together. [/LIST] The only other potentially relevant detail is that about two months ago, we had mains supply issues. Voltage would drop enough to cause lights to dim and flicker (actually, constantly flicker at times). Some neighbours (no C-Bus) reported the same issue. Once the power company fixed a dodgy connection at the pole, the issue stopped. They confirmed it was just affecting the one phase, which my house happened to be on. Don't know if the under-voltage could do any damage. Anyway, sorry for the essay (I work in software development and appreciate detailed bug reports...) My expectation is that the 5512RVF needs to be replaced, and possibly the dimmer. But thought I'd put it out there in case there is something else that I've missed. Thanks in advance. Paul