Has any one come across what appears to be a problem with the Homegate 3.7 and the colour touch screen. What I have found is any scene that ramps GA's to 0% over a set time of say 1min has big problems. What happens is that any GA that were at 100% before the scene was run get ramped to 1% where they stay for what seems to be a ramdom time of anywhere from an extra one minute right up to three minutes. After this random time is reached the GA then turn off to 0%. If their is a trigger used for the scene this gets set to 100% and that is where it stays. This creates a problem if you are useing a bell press mech to remote trigger the scene due to the fact that the first time the key input is pressed it does not trigger the scene because the touch screen left the trigger GA at 100%. The second time the key input is pressed the scene then is trigged as it should have been the first time it was pressed. The problem of the GA getting ramped to 1% also affects the system if you have set up you key switch as memoory dimmers because the next time you press the memory dimmer that is controlling one of the GA that got ramped tyo 1% it goes staright back to 1% (a real pain in the ass). The only way you can see all of the above is if you run the toolkit application log while the scene is being run. This problem also has many other implicatins to the c-bus system. If you don't belive me grab a colour touch screen make a new project and track what happens in the application log on Toolkit. The Application log on the touch screen shows everything as normal (but it lies). :(