Load monitor

Discussion in 'C-Touch/HomeGate/SchedulePlus/PICED Software' started by JasonCox, Oct 10, 2005.

  1. JasonCox

    JasonCox

    Joined:
    Aug 17, 2004
    Messages:
    75
    Likes Received:
    0
    I am using the Load Monitor on the colour touchscreen for some important c-bus levels. I find that the levels are saved from the laptop before the project is transfered ok. When I try to test if it is working on the colour touchscreen by changing the c-bus levels and resetting the unit, The levels come back as they were when the project was uploaded.

    How can I make the colour touch screen save the levels?

    I have tried putting a button in for the load monitor and it says that the levels should be saved and I have even tried ticking Auto update (which doesn't get saved on a reset or upload) but to no luck :(
     
    JasonCox, Oct 10, 2005
    #1
  2. JasonCox

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    It only saves the levels every few minutes, otherwise it would be continually writing to disk as levels change. Try changing the levels, wait for 5 minutes and then reset the unit.
     
    Darren, Oct 17, 2005
    #2
  3. JasonCox

    JasonCox

    Joined:
    Aug 17, 2004
    Messages:
    75
    Likes Received:
    0
    Ahhh, thanks for that Darren, I am not usually patient enough to wait 5 minutes while testing :D
     
    JasonCox, Oct 18, 2005
    #3