Lights group flashes 3 times 5 secs apart

Discussion in 'General Discussion' started by Gilly, Feb 20, 2019.

  1. Gilly

    Gilly

    Joined:
    Feb 20, 2019
    Messages:
    4
    Likes Received:
    0
    Hi and thanks,
    For many months when switched on our hall lights (7 in the group) will flash 3 times 5 seconds apart and then stay off.
    Then for a few months they'll work fine.
    We bought the house with cbus in it. Installed about 1999.
    What does this mean? How can I fix?
     
    Gilly, Feb 20, 2019
    #1
  2. Gilly

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,420
    Likes Received:
    62
    Location:
    Adelaide
    That sounds like what happens with a Universal Dimmer when there is an overcurrent detected... when an incandescent lamp fails often it creates an overcurrent situation, which causes the dimmer channel to shut down. It will try 3 times to restart the channel and then give up if not successful.

    What type of lamps are you using? What's the total load (in Watts) on the channel.

    Nick
     
    NickD, Feb 20, 2019
    #2
  3. Gilly

    Gilly

    Joined:
    Feb 20, 2019
    Messages:
    4
    Likes Received:
    0
    I'm sure you are correct - thanks Nick.
    I have 7x50W Dichroic downlight globes.
    If I remove 5 globes the last 2 stay on.
    I've tried to find out which lamp offends but it doesn't matter which globes I leave out and in which sockets, 2 globes stay on, 3 leads to flashing then off.
    Should I just replace them with 7W LED globes?
     
    Gilly, Feb 20, 2019
    #3
  4. Gilly

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,420
    Likes Received:
    62
    Location:
    Adelaide
    That loading should be ok, and it should definitely be OK with just 3 of them..

    Just re-reading... if it was installed in 1999 it wouldn't be a Universal dimmer (they didn't come out until 2006ish).

    How many channels on the dimmer? What does it say on the front? (Is it a DIN rail mounting dimmer?).

    Nick
     
    NickD, Feb 21, 2019
    #4
  5. Gilly

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    assuming that its NOT a universal dimmer based on the age of the install, then 7 x 50W is too high.

    200W max per 1A channel is the rule of thumb I work to (240W resistive load in basic numbers - and yeah I know we should work on 230V not 240V - just keeping it simple).

    If its a four channel dimmer @ 2A/channel then 7 is fine.

    3 should work OK as this is only 150W.

    Nick can answer this - what is the effect of exceeding capacitance?
     
    znelbok, Feb 21, 2019
    #5
  6. Gilly

    Gilly

    Joined:
    Feb 20, 2019
    Messages:
    4
    Likes Received:
    0
    Sorry for the delay and thanks for your help & interest.
    The dimmer's description is -
    DIMDU4 - DIN Rail 4 Channel Universal Dimmer, 2A per channel

    Incidentally I did try the 7x 7W LED globes and they work (without flashing) but are not as bright or as good as the 50W.

    Any suggestions?
    I don't need them to be dimmable.
     
    Gilly, Feb 28, 2019
    #6
  7. Gilly

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,420
    Likes Received:
    62
    Location:
    Adelaide
    The universal dimmer should be fine with that load.

    What does the indicator (on the dimmer) for the channel that has the problem do after it's flashed 3 times and turned off? Is is flashing green or flashing orange/green?

    Nick
     
    NickD, Feb 28, 2019
    #7
  8. Gilly

    Matthew

    Joined:
    Oct 26, 2007
    Messages:
    260
    Likes Received:
    1
    Location:
    Adelaide
    I recommend have the downlights changed to dedicated LED types. Be careful to get ones that are suitable for C-Bus (LED's with a separate driver is a good indicator, all in one /integrated units are more problematic in my experience) or there may be turn off issues.
    The LED lamps whilst often advertised as equivalent, are usually less output than the halogen. That said, I've found the Osram ones to be the best / brightest & most reliable.
     
    Matthew, Mar 19, 2019
    #8
  9. Gilly

    Gilly

    Joined:
    Feb 20, 2019
    Messages:
    4
    Likes Received:
    0
    Thank you very much.
    Yes, the LED ones I have are not as bright and I will change the downlights as you suggest.
     
    Gilly, Mar 19, 2019
    #9