Heat dissipation

Discussion in 'General Discussion' started by bijoykr, Jan 15, 2009.

  1. bijoykr

    bijoykr

    Joined:
    Aug 27, 2007
    Messages:
    38
    Likes Received:
    0
    Location:
    INDIAN living in QATAR
    Dear Friends,

    Do any where mentioned about the exact heat dissipated from architectural 16A dimmer. If there is any calculation sheet available please let me know. The client is calculating the total heat dissipation in the electrical room(ie all low voltage and extra low voltage equipments including audio video equipments) . All other people gave them the details of maximum heat dissipation from the respective components. We too need to give an answer with some write up or calculation details.
    Please help to give a proper answer to our client.

    Thanks & regards

    Bijoy
     
    bijoykr, Jan 15, 2009
    #1
  2. bijoykr

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    There are figures for power dissipation per channel at 50% and 100% output in the Installation instructions.

    Is this not sufficient?

    Nick
     
    NickD, Jan 15, 2009
    #2
  3. bijoykr

    bijoykr

    Joined:
    Aug 27, 2007
    Messages:
    38
    Likes Received:
    0
    Location:
    INDIAN living in QATAR
    Thanks Nick,
    Can you help me to know about the power dissipation at lower output, will it increase the power dissipation than at the rate 50%

    Thanks in advance
     
    bijoykr, Jan 19, 2009
    #3
  4. bijoykr

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,398
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    The installation instructions and spec sheet are the authoritative data.

    You will see that the dissipation per channel is highest at 50% brightness.

    In general, the dissipation is highest at approximately 50% brightness (for all dimmers, not just Clipsal.) This means that for a brightness less than 50% the dissipation will decrease. Exactly how much is hard to say. For a small brightness, the dissipation will be somewhere between the quoted "off state" dissipation, and the 100% on-state dissipation.

    If you assume that the per-channel dissipation is highest for the 50% brightness case then you will have the worst-case heat-load condition covered, and for other brightness settings the dissipation in general should be less.

    ------------

    Note for the picky or pedantic: the worst case power dissipation of dimmers occurs in general at a 50% conduction angle. However, the exact conduction angle of maximum dissipation will depend on the exact dimmer design. Some dimmers have highest dissipation at 45%, some at 50%, some at 55%, some at 60%. It depends on the design. Usually the manufacturer will quote a maximum dissipation per channel (and the conditions under which that occurs) as well as dissipation under some other conditions.
     
    ashleigh, Jan 19, 2009
    #4
  5. bijoykr

    bijoykr

    Joined:
    Aug 27, 2007
    Messages:
    38
    Likes Received:
    0
    Location:
    INDIAN living in QATAR
    Thanks alot.

    now its crystal clear
     
    bijoykr, Jan 19, 2009
    #5