    Not sure if these are used in Oz, but we have a number of projects where the client want GU or GZ10 Mains Halogen downlights/spotlights etc.

    On normal wall mounted dimmers we have to derate the dimmer by 50%, i.e. 4 x 50w Mains Halogen requires 400w Dimmer to control.

    Is there any issues like this with the DIN Dimmer modules ?

    We usually get the clients to have LV Halogen, but on this particular project the client has chosen surface GZ10 spots that are mounted off an oak beam.

    I certainly dont want to try putting 4 to every single 1a channel if it causes a problem, and likewise dont want to quote twice the size for every circuit if not necessary.

    Any help appreciated.




    Dean.
     
    Rolecgroup, Apr 28, 2005
    #1
  2. Rolecgroup

    furlong

    Joined:
    Oct 29, 2004
    Messages:
    13
    Likes Received:
    0
    Dean

    for what it is worth I have two banks of 4 x 50w Gu10s and two banks of 3 x 50w Gu10s all running off 8channel 1amp dimmers and have had no problems in the past 18 months.

    I am not a sparks so I can't comment on safety etc but it works fine.

    Regds
    Mick
     
    furlong, Apr 28, 2005
    #2
  3. Rolecgroup

    dbuckley

    Joined:
    Oct 11, 2004
    Messages:
    39
    Likes Received:
    0
    Location:
    North Canterbury, New Zealand
    Dean

    Why do you need to derate? Are these not just standard incandecent lamps, albeit halogens?
     
    dbuckley, Apr 28, 2005
    #3
  4. Rolecgroup

    rhamer

    Joined:
    Aug 3, 2004
    Messages:
    673
    Likes Received:
    3
    Location:
    Melbourne, Australia
    rhamer, Apr 28, 2005
    #4
  5. Rolecgroup

    Nick Mullins

    Joined:
    Aug 3, 2004
    Messages:
    51
    Likes Received:
    0
    Silly clients know best

    gay dean, be sure to install those 240v halogens in a accessible area.you be forever there changing globes and listening to a client complain that the globes say 4000 hours on the box and they are always blowing after a couple of weeks.they create alot of heat that seems to affect globe life.Your local commercial light rep would be able to provide backing evidence.they are just not made for long hours of use.But thats only my 2 bobs worth. :)
     
    Nick Mullins, Apr 29, 2005
    #5
  6. Rolecgroup

    Rolecgroup

    Joined:
    Aug 3, 2004
    Messages:
    69
    Likes Received:
    0
    Mick

    Good to know you've had them working ok for that length of time - that puts my mind at rest.

    DBuckley

    Dont know why we derate, but all the big manufacturers in the UK - MK, MEM Home Automation tells us we have to, and from personal experience :) before this was made common knowledge i had a 250w dimmer fail twice which was controlling 4 x 50w Mains Halogen :mad:

    Rohan

    Thanks for that - confirms its ok - i only searched from GZ10 or GU10....

    Nick

    Unfortunately i'm very aware of the lamp problem. We moved from LV to Mains Halogen a number of years ago when philips were first pushing them. We were installing around 2500 fitting per year and the failure rate was appauling, either straight out the box, or after a short period of time.

    What came to light is that the Mains Halogen manufacturers show a SUGGESTED lamp life i.e. 2.5k hours, rather the LV who give a guaranteed life of upto 5k hours. These fittings are actually going to be in a real git of a location off a couple of oak beams two storeys up. I'm currently actively looking for a similar fitting to that chosen that is available in LV. Problem is its going to need an integrated Transformer as its a surface fitting, and most of those i've come across dont dim :confused:



    Dean.
     
    Rolecgroup, Apr 29, 2005
    #6
  7. Rolecgroup

    Thomas

    Joined:
    Nov 25, 2004
    Messages:
    252
    Likes Received:
    0
    A bit of info

    Hi everyone,
    I would like to provide some info on the issue of 240V vs 12V dichroic, or otherwise light sources. Having worked for a couple of years at Osram in the Tech department, I do know one or two things. Facts are as follows:

    - the Mains Halogens behave exactly like incandescent lamps, except that lamp life is a bit better.

    - lamp life of Mains halgens is only marginally better than incandescents, depending on the filament rating vs actual supply voltage at site.

    - LV halogens are rated 4000 or 5000h average expected life, vs 1000 or 2000h for the mains voltage version.

    - light output of the Mains version is no more than one third of it's LV counterpart .... think of replacement frequency here

    - at the same time, dimming ANY filament type of lamps by only 5% will increase it's life by a factor 2.

    - Cost of the Mains version vs LV version of dichroics is a factor 2 to 3 (in this country).

    Looking at the above, it would make sense not to recommend such a light source (Mains), except for areas such as walk-in cubboards, pantry's, or any other short-run-time areas.

    In summary, as regards the dimmer, the Mains version of whatever halogen or incandescent lamps you use, will allow you to utilise the full rated capacity of the dimmer (leading or trailing edge), only if you use LV versions must you heed the type and model of transformer used, and de-rate your dimmer in accordance with the schedule issued by Clipsal.

    Hope this helps,

    Regards
    Thomas
     
    Thomas, Apr 29, 2005
    #7
  8. Rolecgroup

    Nick Mullins

    Joined:
    Aug 3, 2004
    Messages:
    51
    Likes Received:
    0
    Theres LV Out there

    Dean
    Have found crompton lighting have some good quality fittings with a electronic lv trani for each track head pretty reasonably priced . i have used these and found them to work great and this would solve all your problems :)
     
    Nick Mullins, Apr 29, 2005
    #8
  9. Rolecgroup

    UncleDick

    Joined:
    Aug 5, 2004
    Messages:
    130
    Likes Received:
    0
    Location:
    Adelaide
    I have seen Mains Halogens used on conventional and C-bus dimmers in OZ and O/S since ~2000 never heard of any de-rating issues. Dimmer sees them as an incandescent type load (ie 0Ohms cold resistance rising rapidly as power flows). Interested to hear from any one who has details of why derating is required.
     