Getting the Red Hand etc

Discussion in 'C-Bus Wiser 1 Controller' started by homer51502001, Oct 7, 2012.

  1. homer51502001

    homer51502001

    Joined:
    Mar 13, 2011
    Messages:
    2
    Likes Received:
    0
    Location:
    Sydney
    Hi guys, I recently upgraded firmware on the Wiser, thinking that it might be a good idea etc. I have factory reset back to 192.168.2.1, direct connect via ethernet, still getting the old Red Hand of no comms. Unit is responding I can extract the old config using 192.168.2.1 address but unable to bring up any config window to reconfigure the Wiser unit back to its correct LAN address.

    Thanks.
     
    homer51502001, Oct 7, 2012
    #1
  2. homer51502001

    bmerrick

    Joined:
    Jun 13, 2007
    Messages:
    434
    Likes Received:
    34
    Location:
    Sydney
    bmerrick, Oct 7, 2012
    #2
  3. homer51502001

    kjayakumar

    Joined:
    Oct 27, 2008
    Messages:
    448
    Likes Received:
    0
    Here's what I would do:
    - as Brad mentioned, verify that the setup pages are accessible via http://192.168.2.1/index_i.htm
    - verify that the PICED project that is loaded on to the unit has matching settings as configured via the Wiser's setup pages. This means that if you have set the Wiser unit's IP to 192.168.2.1, then the PICED project that you wil ltransfer has details section for lan with the same 192.168.2.1. The CNI will need to be accessible, eg: 192.168.2.2.
     
    kjayakumar, Oct 7, 2012
    #3
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.