    I have a fan in a boiler room and I need to operate it several times every day.
    Is there a way, without logic, to change the duration time of a schedule?
    Only a 5080TC on site. I could create 2 schedules Fan ON and Fan OFF witch will be repeated during the day, however I was wondering if there is a more user friendly way to succeed this.
     
    2SC, Jul 17, 2011
    #1
  2. 2SC

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    You could use a "pulsed group" in a Schedule. This will halve the number of Schedules.

    You could also use repeat Schedules - for example, every 2 hours between 9 AM and 7PM. This will reduce the number of Schedules even more.

    You can use in-built System IO variables to allow the user to edit the Schedules. See the Schedule editing template for ideas.
     
    Darren, Jul 18, 2011