Edlt no serial number in toolkit unable to open

Discussion in 'C-Bus Wired Hardware' started by ian rockett, Oct 21, 2022.

  1. ian rockett

    ian rockett

    Joined:
    Dec 13, 2004
    Messages:
    24
    Likes Received:
    2
    Location:
    Bournemouth UK
    I am now replacing a 3rd Edlt that has just gone blank (fitted 2016) the new switch will not program. It can be seen in toolkit but will not load. Also showing no serial number. 2 fatal messages come up
    90FA0EDC-D620-4525-A650-6E9ABFD7D864.jpeg
    5B1F3AFC-8AFC-4094-8979-FE69F1CF12CF.jpeg
    I have tried 2 units with the same results
     
    ian rockett, Oct 21, 2022
    #1
  2. ian rockett

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    759
    Likes Received:
    67
    Location:
    Adelaide, South Australia
    Had the similar this week on a site with new eDLTs. Latest Toolkit (V1.16.2) has given me grief. Also reporting firmware wrong firmware version (showing 1.6 instead of 5.5.00. Rolled back to V1.16.0 ( had to roll back cgate too) and it 'sorta' worked. Not getting the same on my existing home network. Haven't tried a new eDLT unit on the home one yet. I'll try over the weekend
     
    Conformist, Oct 22, 2022
    #2
  3. ian rockett

    ian rockett

    Joined:
    Dec 13, 2004
    Messages:
    24
    Likes Received:
    2
    Location:
    Bournemouth UK
    I running 1.15.7 so I don’t think that is the issue. Also tried to update firmware and it will not load.
    Thanks for replying
     
    Last edited: Oct 22, 2022
    ian rockett, Oct 22, 2022
    #3
  4. ian rockett

    mattyb

    Joined:
    Jul 29, 2005
    Messages:
    78
    Likes Received:
    0
    Location:
    Sydney, Australia
    Hey Ian, we had this issue - if it's a new eDLT I think you will need at least Toolkit 1.16.0. Should solve that problem...no doubt will introduce others!! :)
     
    mattyb, Oct 23, 2022
    #4
  5. ian rockett

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    759
    Likes Received:
    67
    Location:
    Adelaide, South Australia
    After spending quite a bit of time trouble shooting, you need to be running the latest Toolkit (V1.16.2) and make sure CGate is cleaned out properly by checking the 'Remove any old C-Gate files...' checkbox during installation.
    upload_2022-10-23_16-48-55.png



    I didn't do this previously and it has caused me no end of pain. There must have been a rogue legacy file in there somewhere.

    After completing this, my systems both locally and remotely are working with eDLTs
     
    Conformist, Oct 23, 2022
    #5
  6. ian rockett

    ian rockett

    Joined:
    Dec 13, 2004
    Messages:
    24
    Likes Received:
    2
    Location:
    Bournemouth UK
    Bingo thank you. Upgrading toolkit sorted it, not that it was easy to find but up and running now.
     
    ian rockett, Oct 23, 2022
    #6
    Conformist likes this.