    Let's get a group to turn on when triggered by a PIR at different levels during a given day.

    I've had several goes at this over the years. So sharing my latest NAC/SHAC/AC2 LUA code.

    I mostly use this for a hall group, designed to turn on at a lower level in the evening so as to not disturb anyone sleeping with a door ajar. Other PIRs are configured so as not to blind you when coming in from the dark. Also used for carport lights, and late night snacking in the pantry...

    Enjoy. Two scripts.

    Resident zero delay:
    Code:
    --[[
    Dynamic triggered light level
    -----------------------------
    
    Notes:
    
    At sunrise the target level is set to high, then lowered at a specified evening time, then lowered
    again at a subsequent time or when a late night scene is set. When the optional 'scene' is set then
    the target level will be immediately set to super-low. The late night scene is triggered elsewhere
    (a key?).
    
    If the group is manually set to off (or by a scene), then control of the group by this script will
    suspend for a given 'egress' to allow for area egress with the PIR disabled.
    
    If the group is manually set to a level other than the script target (like with a switch timer) then
    this script will not turn it off after the timer runtime. To re-enable the timer function the group
    must be switched to off.
    
    A PIR to turn on the group should be configured to pulse a trigger group for approx one second, and
    also have an enable group for that PIR defined.
    
    Run it as a resident script with zero delay (it uses socket timeout to be a super-low CPU user).
    
    Set keywords for the trigger group, which will be read by this script.
      DPIR (mandatory)
      grp= Group to control (mandatory)
      en= Enable group (mandatory)
      run= Runtime
      lv= Dynamic levels - 3x separated by slash = daytime/low/super-low (super-low optional)
      hr= Hour transitions - 2x sep by / = hour-for-low/hour-for-super-low (super-low optional)
      ramp= Ramp rate - 2x sep by / = ramp-on/ramp-off
      dd= Seconds to allow for egress (disable duration)
      scene= Name of a late night scene (when set make immediate switch to super-low dynamic level)
    Defaults noted below.
    
    Keyword examples, applied to each PIR trigger group:
    
    DPIR, grp=Hall Mid Pendants, en=Hall PIR_1 Enable, run=90, lv=127/89/31, hr=22/0, ramp=4/12, dd=15, scene=Late night,
    DPIR, grp=Hutch Bathroom, en=Hutch Bathroom PIR Enable, run=300, lv=179/127, hr=22, ramp=0/12, dd=5,
    DPIR, grp=Outside Carport, en=Outside Carport Enable, run=120, lv=205/153, hr=22, ramp=4/8, dd=15,
    DPIR, grp=Kitchen Pantry LV, en=Kitchen Pantry PIR Enable, run=60, lv=240/180/80, hr=22/0, ramp=0/20, dd=0,
    
    Changes to keywords are not detected (to improve performance), and require a resident script re-start,
    and also a restart of the DPIR event-based script for newly added DPIR keywords.
    --]]
    
    logging = false
    defaultRun = '120'; defaultLv = '210/127/127'; defaultHr = '22/0'; defaultRamp = '4/8'; defaultDd = '15'; defaultScene = '' -- Defaults for trigger groups
    socketTimeout = 1.0 -- Inbound DPIR messages will be handled near instantly, and other script tasks will occur approx every second
    
    --[[
    UDP listener - receive messages from the event script 'DPIR'
    --]]
    
    server = require('socket').udp()
    server:settimeout(socketTimeout)
    server:setsockname('127.0.0.1', 5431) -- Listen on port 5431 for PIR triggers
    
    --[[
    Utility functions
    --]]
    
    function logif(msg) if logging then log(msg) end end
    
    require('uci')
    function calculateSunriseSunset() sunrise, sunset = rscalc(tonumber(uci.get('genohm-scada.core.latitude')), tonumber(uci.get('genohm-scada.core.longitude'))) end
    
    function isEmpty(s) return s == nil or s == '' end
    
    timer = {}
    function timerStart(alias) timer[alias] = { ['timerStarted'] = os.time(), ['timerDuration'] = pirs[alias]['runtime'] } end
    function timerStop(alias) timer[alias] = { ['timerStarted'] = 0, ['timerDuration'] = 0 } end
    function timerStarted(alias) return timer[alias]['timerStarted'] ~= 0 end
    function timerExpired(alias) return (timer[alias]['timerStarted'] == 0) or (os.time() - timer[alias]['timerStarted'] >= timer[alias]['timerDuration']) end
    
    function simulateTrigger(pir) PulseCBusLevel(pir['net'], pir['app'], pir['dTrigger'], 255, 0, 1, 0) end -- Simulate a PIR trigger
    
    --[[
    Initialisation
    --]]
    
    local grps = GetCBusByKW('DPIR', 'or')
    local found = {}
    local n = 0
    pirs = {}
    
    for k, v in pairs(grps) do
      local error = false
      local run = defaultRun; local lv = defaultLv; local hr = defaultHr; local ramp = defaultRamp; local dd = defaultDd; local scene = defaultScene -- Reset to defaults
      local net = v['address'][1]; local app = v['address'][2]; local group = v['address'][3]
      local alias = net..'/'..app..'/'..group
      pirs[alias] = {}
    
      for _, t in ipairs(v['keywords']) do
        tp = string.split(t, '=')
        tp[1] = trim(tp[1])
        if tp[2] then
          tp[2] = trim(tp[2])
          if tp[1] == 'grp' then target = tp[2]
          elseif tp[1] == 'en' then en = tp[2]
          elseif tp[1] == 'run' then run = tp[2]
          elseif tp[1] == 'lv' then lv = tp[2]
          elseif tp[1] == 'hr' then hr = tp[2]
          elseif tp[1] == 'ramp' then ramp = tp[2]
          elseif tp[1] == 'dd' then dd = tp[2]
          elseif tp[1] == 'scene' then scene = tp[2]
          end
        end
      end
      pirs[alias] = {
        ['net'] = net,
        ['app'] = app,
        ['dGroup'] = GetCBusGroupAddress(net, app, target),
        ['dTrigger'] = group,
        ['dTriggerEn'] = GetCBusGroupAddress(net, app, en),
        ['runtime'] = tonumber(run),
        ['egress'] = tonumber(dd),
        ['scene'] = scene
      }
      local parts
      parts = string.split(lv, '/')
      if #parts == 3 then
        pirs[alias]['levelHigh'] = tonumber(parts[1])
        pirs[alias]['levelLow'] = tonumber(parts[2])
        pirs[alias]['levelSuperLow'] = tonumber(parts[3])
      elseif #parts == 2 then
        pirs[alias]['levelHigh'] = tonumber(parts[1])
        pirs[alias]['levelLow'] = tonumber(parts[2])
        pirs[alias]['levelSuperLow'] = pirs[alias]['levelLow']
      else
        log('ERROR: Need two or optionally three parts for "lv" keyword of '..alias..' (high/low/optional super-low)')
        error = true
      end
      parts = string.split(hr, '/')
      if #parts == 2 then
        pirs[alias]['hourLow'] = tonumber(parts[1])
        pirs[alias]['hourSuperLow'] = tonumber(parts[2])
      elseif #parts == 1 then
        pirs[alias]['hourLow'] = tonumber(parts[1])
        pirs[alias]['hourSuperLow'] = 0
      else
        log('ERROR: Need at least one part for "hr" keyword of '..alias..' (hour-low/optional hour-super-low)')
        error = true
      end
      parts = string.split(ramp, '/')
      if #parts == 2 then
        pirs[alias]['rampOn'] = tonumber(parts[1])
        pirs[alias]['rampOff'] = tonumber(parts[2])
      else
        log('ERROR: Need two parts for "ramp" keyword of '..alias..' (ramp on/ramp off)')
        error = true
      end
      if error then pirs[alias] = nil end
    end
    
    calculateSunriseSunset()
    
    now = os.date('*t')
    nowMinute = now.hour * 60 + now.min
    lastMinute = -1
    
    for k, pir in pairs(pirs) do
      timerStop(k)
    
      pir['target'] = pir['net']..'/'..pir['app']..'/'..pir['dGroup']
      SetCBusState(pir['net'], pir['app'], pir['dTriggerEn'], true)
      pir['dynamicSet'] = pir['levelHigh']
    
      if pir['hourLow'] * 60 > sunrise then -- i.e. Low is before midnight
        pir['dynamicSet'] = pir['levelSuperLow']
        if nowMinute >= sunrise then pir['dynamicSet'] = pir['levelHigh'] end
        if now.hour >= pir['hourLow'] then pir['dynamicSet'] = pir['levelLow'] end
        if pir['hourSuperLow'] > pir['hourLow'] and now.hour >= pir['hourSuperLow'] then pir['dynamicSet'] = pir['levelSuperLow'] end -- For super-low before midnight too
      else -- Low is after midnight
        pir['dynamicSet'] = pir['levelHigh']
        if nowMinute < sunrise then
          if nowMinute >= pir['hourLow'] * 60 then pir['dynamicSet'] = pir['levelLow'] end
          if nowMinute >= pir['hourSuperLow'] * 60 then pir['dynamicSet'] = pir['levelSuperLow'] end -- Super-low must be after low
        end
      end
    
      log(
        'Initialised DPIR target '..pir['target']..
        ', dynamic level ' .. pir['dynamicSet']..
        ', levels='..pir['levelHigh']..'/'..pir['levelLow']..'/'..pir['levelSuperLow']..
        ', hours='..pir['hourLow']..'/'..pir['hourSuperLow']..
        ', ramps='..pir['rampOn']..'/'..pir['rampOff']
      )
      if GetCBusLevel(pir['net'], pir['app'], pir['dGroup']) == pir['dynamicSet'] then -- If the group is currently at the dynamic level then start the timer
        logif(pir['target']..' at desired level, so starting timer')
        timerStart(k)
      end
      pir['lateNightSet'] = false
      pir['suspended'] = nil
      pir['oldGroupLevel'] = GetCBusLevel(pir['net'], pir['app'], pir['dGroup'])
    end
    
    
    --[[
    PIR trigger processing
    --]]
    
    function processTrigger(alias)
      local target = pirs[alias]['target']
      if not pirs[alias]['suspended'] then
        if timerStarted(alias) then
          logif(target..' triggered, reset timer')
          timerStart(alias) -- Reset the timer if already running
        else
          local net = pirs[alias]['net']; local app = pirs[alias]['app']; local group = pirs[alias]['dGroup']; local dynamicSet = pirs[alias]['dynamicSet']
          groupLevel = GetCBusLevel(net, app, group)
          logif(target..' current level '..groupLevel)
          if groupLevel == 0 or groupLevel == dynamicSet or pirs[alias]['rampingOff'] then -- Turn on the group and start the timer
            logif(target..' triggered, turning on')
            SetCBusLevel(net, app, group, dynamicSet, pirs[alias]['rampOn'])
            groupLevel = dynamicSet
            timerStart(alias)
            pirs[alias]['rampingOff'] = false
          else
            logif(target..' was not turned on, dynamicSet='..pirs[alias]['dynamicSet']..', rampingOff='..tostring(pirs[alias]['rampingOff']))
          end
          pirs[alias]['groupLevel'] = groupLevel
        end
      else
        logif(target..' suspended, doing nothing')
      end
    end
        
        
    --[[
    Main loop
    --]]
    
    while true do
      -- Check for new triggers
      received = server:receive() -- Get trigger message, with timeout ... message is processed after checks below
    
      now = os.date('*t'); nowMinute = now.hour * 60 + now.min
    
      for alias, pir in pairs(pirs) do
        -- GET THE STATE OF GROUP
        if GetCBusTargetLevel(pir['net'], pir['app'], pir['dGroup']) == GetCBusLevel(pir['net'], pir['app'], pir['dGroup']) then
          groupLevel = GetCBusLevel(pir['net'], pir['app'], pir['dGroup'])
        else
          groupLevel = pir['oldGroupLevel']
        end
     
        if not pir['suspended'] then -- Suspension occurs to allow egress
          if (groupLevel ~= pir['oldGroupLevel']) then
            -- logif('Group change, old='..pir['oldGroupLevel']..', new='..groupLevel)
            pir['oldGroupLevel'] = groupLevel
            groupChange = true
          else
            groupChange = false
          end
    
          -- CHECK FOR TIMER EXPIRY
          if timerStarted(alias) then
            if timerExpired(alias) then
              logif(pir['target']..' timer expired')
              if groupLevel == pir['dynamicSet'] then
                logif(pir['target']..' ramping off')
                SetCBusLevel(pir['net'], pir['app'], pir['dGroup'], 0, pir['rampOff'])
              else
                logif(pir['target']..' at unexpected level ('..groupLevel..', expected '..pir['dynamicSet']..'), doing nothing (re-switching off if already off)')
                if not groupLevel then SetCBusState(pir['net'], pir['app'], pir['dGroup'], false) end
              end
              timerStop(alias)
            end
          end
    
          -- CHECK FOR GROUP TURNED OFF
          if groupChange and groupLevel == 0 and timerStarted(alias) then
            logif(pir['target']..' has been turned off')
            if GetCBusState(pir['net'], pir['app'], pir['dTriggerEn']) then
              PulseCBusLevel(pir['net'], pir['app'], pir['dTriggerEn'], 0, 0, pir['egress'], 255)
              logif(pir['target']..' stopping timer and delaying '..pir['egress']..' seconds')
              timerStop(alias)
              pir['suspended'] = os.time() -- Suspend trigger detection until the end of the disable duration, as no point running
            end
          end
    
          -- DESIRED STATE SENSE
          if groupChange and (GetCBusLevel(pir['net'], pir['app'], pir['dGroup']) == pir['dynamicSet']) then
            logif(pir['target']..' is at desired level of '..pir['dynamicSet'])
            if not timerStarted(alias) then
              logif(pir['target']..' turned on at target level, so simulating PIR trigger')
              simulateTrigger(pir)
            end
          end
    
        else
          -- PIR IS SUSPENDED...
          if os.time() - pir['suspended'] >= pir['egress'] then
            pir['suspended'] = nil
            logif(pir['target']..' resumed')
          else
            if GetCBusLevel(pir['net'], pir['app'], pir['dGroup']) == pir['dynamicSet'] then -- manually switched on again, so re-trigger
              pir['suspended'] = nil
              logif(pir['target']..' turned on again before egress duration, so re-triggering PIR')
              simulateTrigger(pir)
            end
          end
        end -- if not suspended
    
        -- CHECK FOR LATE NIGHT SCENE SET
        if not isEmpty(pir['scene']) then
          if not pir['lateNightSet'] and SceneIsSet(pir['scene']) then
            pir['lateNightSet'] = true
            pir['dynamicSet'] = pir['levelSuperLow']
            logif(pir['target']..' adjusted for late night mode at level '..pir['dynamicSet'])
            if groupLevel > 0 and timerStarted(alias) then -- Group is on, so adjust it
              simulateTrigger(pir)
              pir['rampingOff'] = true
            end
          else
            if pir['lateNightSet'] and (not SceneIsSet(pir['scene'])) then
              pir['lateNightSet'] = false
              logif(pir['target']..' late night mode off')
              if pir['hourLow'] * 60 > sunrise then -- i.e. Low is before midnight
                if now.hour < pir['hourLow'] then pir['dynamicSet'] = pir['levelHigh'] else pir['dynamicSet'] = pir['levelLow'] end
                if pir['hourSuperLow'] > pir['hourLow'] and now.hour >= pir['hourSuperLow'] then pir['dynamicSet'] = pir['levelSuperLow'] end
              else
                pir['dynamicSet'] = pir['levelHigh']
                if nowMinute < sunrise then
                  if nowMinute >= pir['hourLow'] * 60 then pir['dynamicSet'] = pir['levelLow'] end
                  if nowMinute >= pir['hourSuperLow'] * 60 then pir['dynamicSet'] = pir['levelSuperLow'] end
                end
              end
              logif(pir['target']..' adjusted dynamic level to '..pir['dynamicSet'])
            end
          end
        end
      end -- for alias in
    
      -- PROCESS ANY RECEIVED MESSAGE
      -- Done after checks above, mostly to cater for group manually turned off
      if received ~= nil then processTrigger(received) end
    
      -- ADJUST TARGET GROUP DYNAMIC LIGHT LEVEL
      function setDynamicGroupLevel(pir, level)
        pir['dynamicSet'] = level
        logif(pir['target']..' adjust dynamic level ' .. pir['dynamicSet'])
        if GetCBusLevel(pir['net'], pir['app'], pir['dGroup']) > 0 then -- Lights are on, so set the new level and start the timer
          SetCBusLevel(pir['net'], pir['app'], pir['dGroup'], pir['dynamicSet'], pir['rampOn'])
          simulateTrigger(pir)
        end
      end
      if not setDR and now.min ~= lastMinute then -- check for change every minute
        lastMinute = now.min
        for alias, pir in pairs(pirs) do
          if nowMinute == sunrise then -- Reset to high at sunrise
            setDynamicGroupLevel(pir, pir['levelHigh'])
          end
          if now.min == 0 then -- check transition to low/super low
            local oldLevel = pir['dynamicSet']
            -- Set to low if the right hour, unless already at super-low because of scene trigger
            if now.hour == pir['hourLow'] then if pir['dynamicSet'] ~= pir['levelSuperLow'] then setDynamicGroupLevel(pir, pir['levelLow']) end end
            -- Set to super-low if the right hour
            if now.hour == pir['hourSuperLow'] then setDynamicGroupLevel(pir, pir['levelSuperLow']) end
            if pir['dynamicSet'] ~= oldLevel then log('Adjusted DPIR target '..pir['target']..' dynamic level ' .. pir['dynamicSet']) end
            setDR = true
          end
        end
        if setDR and now.min == 1 then setDR = false end -- Reset the time-based 'set' flag
      end
    
      -- CALCULATE SUNRISE/SUNSET ONCE PER DAY
      if not setSR and now.hour == 1 and now.min == 0 then
        calculateSunriseSunset(); setSR = true
        logif('Sunrise set to: '..sunrise..', and sunset: '..sunset)
      end
      if setSR and now.min == 1 then setSR = false end -- Reset the time-based 'set' flag
    end
    And this triggered on the keyword 'DPIR':

    Code:
    --[[
    Pushes dynamic PIR triggers via internal sockets.
    
    Tag required objects with the "DPIR" keyword and this script will run whenever one of those objects change.
    --]]
    
    logging = false
    
    -- Send an event that a dynamic PIR triggered
    if event.getvalue() ~= 0 then
      require('socket').udp():sendto(event.dst, '127.0.0.1', 5431)
      log('Trigger message for '..event.dst)
    end
     
    ssaunders, Jul 31, 2022
    #1
  2. ssaunders

    ssaunders

    Joined:
    Dec 17, 2008
    Messages:
    246
    Likes Received:
    36
    Location:
    Melbourne
    Note: Code contains a bug. Move this line outside and underneath the if block beginning "if not setDR":
    Code:
      if setDR and now.min == 1 then setDR = false end -- Reset the time-based 'set' flag
    
     
    ssaunders, Aug 1, 2022