downlights

Discussion in 'General Discussion' started by Steve Gray, May 15, 2022.

  1. Steve Gray

    Steve Gray

    Joined:
    Apr 10, 2022
    Messages:
    31
    Likes Received:
    1
    Changing out old halogen dimmable downlights with transformers to new Martec LED dimmable with Dimming LED drivers ( constant current) 10w, tried one before getting to carried away.
    New LED work ok plugging into GPO but when installing into light point in ceiling which has a GPO the light works ok, dims ok but stays luminated slightly with a bit of a flicker when turned off
    Guessing the Cbus system may not like the driver or is it something else?
    Solutions?
     
    Steve Gray, May 15, 2022
    #1
  2. Steve Gray

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    758
    Likes Received:
    67
    Location:
    Adelaide, South Australia
    This is a common problem with many LED downlights. You will need a Load Bypass Device/Load Correction Device (LCD) to be installed across each dimmer channel where the problem occurs. This issue is due to 'off-state leakage' through the dimmer. The LCD will need to be installed by an electrically qualified person as this is deemed to be an alteration to fixed wiring.
     
    Conformist, May 15, 2022
    #2
  3. Steve Gray

    Steve Gray

    Joined:
    Apr 10, 2022
    Messages:
    31
    Likes Received:
    1
    thanks
     
    Steve Gray, May 15, 2022