Disable PIR on shedule

Discussion in 'C-Touch/HomeGate/SchedulePlus/PICED Software' started by Razor2204, Nov 30, 2010.

  1. Razor2204

    Razor2204

    Joined:
    Sep 18, 2010
    Messages:
    15
    Likes Received:
    0
    Location:
    Russian Federation
    hello a PIR sensor 5751LWE is inslalled in cloakroom which is linked to the sleeping room. It sets the light on when you walk in.
    You can also set the light on by switch nearby.

    Is it possible by PAC to disable PIR from 12PM till 7AM and let only switch be functional?
     
    Razor2204, Nov 30, 2010
    #1
  2. Razor2204

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Yes, this is definitely possible, and quite a common thing to do.

    In the configuration of the PIR Sensor, a Group Address can be assigned to the Sensor Enable/Disable function. Configure it so that the PIR is disabled when the Group Address is On.

    In the configuration of the PAC, you need to create a schedule that turns this Group Address On at midnight and Off again at 7AM.

    No change is required in the configuration of the switch.
     
    Newman, Nov 30, 2010
    #2