Detecting LPG bottle changeover

Discussion in 'General Discussion' started by NickD, Aug 10, 2017.

  1. NickD

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,420
    Likes Received:
    62
    Location:
    Adelaide
    Hi All,

    I have bottled LPG at my place, and would like to have some kind of warning when the automatic changeover has happened.

    Obviously this is easy enough to get into C-Bus with a bus coupler but the question of how to sense it and convert to a contact closure remains..

    The current changeover valve has a red flag which is supposed to show when it happens, and I have pondered trying to detect this, but the flag itself has never worked particularly reliably. There are other valves which appear to have different types of flag which might work better or be easier to detect, but they would still require some kind of modification (magnet glue to it, or some kind of colour sensor). A changeover valve with a dry contact output would be perfect but I've not been able to find one so far (I am searching again in parallel with writing this post).

    Has anyone solved this problem before?

    Nick
     
    NickD, Aug 10, 2017
    #1
  2. NickD

    rhamer

    Joined:
    Aug 3, 2004
    Messages:
    673
    Likes Received:
    3
    Location:
    Melbourne, Australia
    An idea out of left field.

    The gas line that has gas flowing through it will be colder than the one that doesn't.
    Stick a couple of temp sensors on each bottle line and the colder one will be the active bottle.
    The rest is just a bit of PAC logic :)

    Cheers

    Rohan
     
    rhamer, Aug 10, 2017
    #2
  3. NickD

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Hi NickD
    Did you check Australian Standards with regard to having any electrical equipment near the cylinders?
    It sounds like quite a task to ensure it will be compliant.
    The people probably best placed to advise would be the gas suppliers.
    Maybe some sort of approved electronic metering system would be the thing to look for.
     
    Last edited by a moderator: Aug 11, 2017
    DarylMc, Aug 11, 2017
    #3
  4. NickD

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,420
    Likes Received:
    62
    Location:
    Adelaide
    Yes..

    AS/NZS 5601 (Gas Installations) specifies clearances around the cylinders, from things like combustible materials and ignition sources. The definition for an ignition source includes any electrical equipment not designed for hazardous areas, so yes, anything homebrew would be difficult to make compliant.

    The clearance required by this is only 500mm above the cylinder though, so if a changeover regulator with built in contacts existed, it could be connected to a bus coupler which itself could be placed outside the restricted zone.

    I realise I could a gas supplier, but I figured it was easier to ask here first :)

    Nick
     
    NickD, Aug 11, 2017
    #4
  5. NickD

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    AS3000 has clearances too.
    I reckon nothing other than something the gas companies can provide would be worth the trouble.
    Metering would actually be a nice touch and also give you the info you are looking for.
    If such a thing existed.
     
    Last edited by a moderator: Aug 11, 2017
    DarylMc, Aug 11, 2017
    #5
  6. NickD

    Wonkey

    Joined:
    Aug 3, 2004
    Messages:
    395
    Likes Received:
    37
    Location:
    Adelaide
    How about a weight sensor and feed it into general input unit.
    Cou would have to make a platform to stand them on.
    Check Ebay as they are many available
    Colin
     
    Wonkey, Aug 11, 2017
    #6
  7. NickD

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Just to mention LPG is a heavier than air gas.
    Anything below the cylinders is also in the prohibited zone.
     
    DarylMc, Aug 11, 2017
    #7
  8. NickD

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Not trying to be a party pooper but whatever you come up with you want to do it properly.
     
    DarylMc, Aug 11, 2017
    #8
  9. NickD

    Ingo

    Joined:
    Dec 2, 2006
    Messages:
    290
    Likes Received:
    1
    Location:
    South Africa
    I used a very simple method, it's called the 'wife sensor'. It might be highly volatile but works 100% of the time. All I did was to close the valve on the second bottle and once the first one was empty I could hear the 'wife sensor' trigger the 'wife siren' and then I just went and opened the second bottle valve :D
     
    Ingo, Aug 11, 2017
    #9
  10. NickD

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Wife sensors have a very short MTBF in cold shower scenarios :)
     
    DarylMc, Aug 12, 2017
    #10
  11. NickD

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    A photo would help heaps in trying to come up with a solution.

    If you can use a simple contact to detect the flag or change over you don't need a certified device (no IECEx or AusEx certificate) but in every case you WILL require a barrier (either a Zener of isolated transformer) which does need a certificate. (this is an Exi - Intrinsically safe install)

    An explosion proof switch would also work (also needs to be certified). This would be an Exd install

    Other methods also exist such as encapsulation, specials and other.

    Understanding the gas class and zoning and method of protection is not a simple task.

    AS3000 calls the hazardous area standards so they are law as well - but just like any electrical install you can take any shortcut you like at your own risk. (I don't advocate doing this unsafely)

    Hope that helps understanding of some of what is involved in doing this simple task.

    Mick
     
    znelbok, Aug 12, 2017
    #11
  12. NickD

    Matthew

    Joined:
    Oct 26, 2007
    Messages:
    260
    Likes Received:
    1
    Location:
    Adelaide
    I like the Temp sensor idea.
    In terms of compliance, C-Bus voltage would be ELV, is it SELV?
    If the Bus coupler was outside the exclusion zone, then only the Temp sensor probes are inside the "gas" zone. The sensors have a 2m tail on them, not sure of the voltage, but AFAIK these are only a few volts.
     
    Matthew, Aug 20, 2017
    #12
  13. NickD

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    Standard does not dictate voltage. Regardless of it is SELV or not (and SELV is for personal protection).

    All instrumentation in a hazardous area (Gas or Dust) is ELV - typically 24VDC. C-Bus is approx 32VDC - so still an issue. Only time it is not an issue is when the voltage is 0...

    Having the temp sensor only in the zone is not sufficient. How do you guarantee that it wont create a spark under a fault condition that will ignite the gas that could be in the area? You can't so it need to be certified - as does the bus coupler.

    You could say that because the gas line is outside in a well ventilated area and that gas goes up/down that the likely hood that gas will be at the sensor in a concentration that is suitable for sustaining a explosion (LEL & UEL) is not possible then you could say it is a non-zoned area, hence no certified devices are required. Better have that documented if it goes bang and show you have the experience to back that decision.

    Thats the hard line approach. Ultimately you can do what ever you like.
     
    znelbok, Aug 22, 2017
    #13
  14. NickD

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,391
    Likes Received:
    24
    Location:
    Adelaide, South Australia
    How about an isolated dc-dc converter to get everything into a total SELV isolated 12V zone.

    Then use one of those photoptic interruptor thingumies that can detect the vane blocking (or passing) a beam of light. Such thingumies are fairly readily available from Digikey.

    A little bit of circuitry can then push an other isolated signal back into something like a bus coupler. Put it all on a small PCB.... bobs yer uncle.

    Use a small microcontroller if it makes like easier.

    I reckon this is a hobby project for a couple of weekends :D
     
    ashleigh, Aug 22, 2017
    #14
  15. NickD

    rhamer

    Joined:
    Aug 3, 2004
    Messages:
    673
    Likes Received:
    3
    Location:
    Melbourne, Australia
    Firstly let me say, I know nothing about the regulations in this situation, so I'm only asking out of interest.

    It appears to me that the apparent danger is the risk of a spark igniting leaking gas. So my question is how does isolating the input voltage eliminate the possibility of a spark?
    I understand it might prevent the blow through of higher voltage coming up the line if the fault is downstream, but even if there is isolation, any voltage could cause a spark couldn't it?

    Rohan
     
    rhamer, Aug 22, 2017
    #15
  16. NickD

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    The use of what is called a barrier limits the amount of energy that can be made available at the device. This energy is not high enough that even if a spark is created it wont ignite the gas. This is called Intrinsically Safe or Exi method.

    You can install your device in a housing that can contain the explosion - what happens here is that when gas is present and a spark does ignite it, the mating surfaces of the lid and any conduit entries are made in such a way that the explosion is contained and any ignited gas that does escape has lost all of its energy through these finely made mating surfaces that it does not have enough energy to ignite the surrounding gasses. This is called Explosion Proof or Exd.

    There are a few others, not quite as common, encapsulation is probably the next. Where you cover the entire devices circuit in say a resin.

    So its not about removing the spark, but rather limiting what the spark can do. In all cases it must not allow the gas in the area to ignite and cause an explosion.

    Hope that helps with the understanding of what this is about.
     
    znelbok, Aug 22, 2017
    #16
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.