Current measurement units on 3 phase

Discussion in 'C-Bus Wired Hardware' started by Charlie Crackle, May 17, 2012.

  1. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Doing a design for a house with 3 phase.

    Customer would like monitoring on

    Property
    AIRCON1
    AIRCON2
    POOL Equip

    All 4 are 3 phase.

    how do I do this and not use up more that 4 energy monitors up in wiser

    1) put all 3 phase cables through the same CT (CT not big enough)

    2) 4 measurement modules with 3 CT per unit one CT on each phase ?
    Can you add 3 together so only uses 1 energy measure channel in wiser ?

    Charles
     
    Charlie Crackle, May 17, 2012
    #1
  2. Charlie Crackle

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    You'll need to measure the 3 phases independently and then calculate the final power figure using logic.

    You should be able to do this by using a bunch of CMU's and having them broadcast their channel current. In logic you should be able to take this information and, along with a line voltage estimate, approximate the actual power.

    Once you've got that, broadcast the result as a new message on the measurement application. bmerrick posted how to do this here.
     
    Newman, May 17, 2012
    #2
  3. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Thanks newman

    I thought as much was hoping I was wrong.

    Wish list for next measurement firmware.... ability to add 3 channels together and send as total

    Charles
     
    Charlie Crackle, May 19, 2012
    #3
  4. Charlie Crackle

    Malcb

    Joined:
    Dec 23, 2011
    Messages:
    4
    Likes Received:
    0
    Location:
    UK
    If all the loads are single phase just measure the neutral current?

    Oops, reading on phone and didnt notice line that said all loads three phase. Power meter sounds best option.
     
    Last edited by a moderator: May 19, 2012
    Malcb, May 19, 2012
    #4
  5. Charlie Crackle

    Don

    Joined:
    Aug 4, 2004
    Messages:
    429
    Likes Received:
    0
    Location:
    Townsville, Australia
    Can't you do this with three CMU's? As long as they're all in close proximity, you can use the fourth channel of each to measure that fourth load's phase.
     
    Don, May 20, 2012
    #5
  6. Charlie Crackle

    [email protected]

    Joined:
    Dec 31, 2009
    Messages:
    55
    Likes Received:
    0
    Location:
    sydney
    If any of the loads are balanced then you just need to measure 1 phase on each of these
     
    [email protected], Jun 2, 2012
    #6