Controling low voltage load

Discussion in 'General Discussion' started by grssll, Nov 21, 2018.

  1. grssll

    grssll

    Joined:
    Jun 13, 2014
    Messages:
    64
    Likes Received:
    0
    Location:
    Sydney
    Hi,
    Does anyone know what type of internal relays Clipsal L5108RELVP have?
    I need to control 48VDC at 1-1.5amp load and I'm not sure if the relay contacts will cope in the long run or I'm better to use L5504RVFC Changeover relay?
    Thanks
     
    grssll, Nov 21, 2018
    #1
  2. grssll

    Damaxx

    Joined:
    May 12, 2008
    Messages:
    228
    Likes Received:
    47
    Had a couple of 48V 3A loads I need to control so used spare channels on my L5108RELVP to control DC relays that could cope with the load. From memory, the contacts in the ELV unit are listed as 30V DC 2A but I have never gutted one to check the physical relays used. For the price of an external relay, figured it wasn't worth destroying a channel.
     
    Damaxx, Nov 21, 2018
    #2
  3. grssll

    grssll

    Joined:
    Jun 13, 2014
    Messages:
    64
    Likes Received:
    0
    Location:
    Sydney
    Then it becomes messy as you double the relays, cables plus a power supply.
    Anyway, inside the Cbus unit is Omron G6CU-2114P relay which is rated at 8A 250AC / 8A 30VDC with maximum switching voltage 125VDC /8A
     
    grssll, Nov 21, 2018
    #3
  4. grssll

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,524
    Likes Received:
    173
    Location:
    Adelaide, Australia
    Assuming you have a resistive load.

    Check out the Maximum Switching Capacity Graph. At 48VDC you have 2 amp resistive, 1 amp inductive. Too close for comfort for me, and you lose your warranty. Take Damaxx's advice, use an external relay and save yourself the future heartache. :)
     
    Ashley, Nov 21, 2018
    #4
  5. grssll

    grssll

    Joined:
    Jun 13, 2014
    Messages:
    64
    Likes Received:
    0
    Location:
    Sydney
    Just to be on the safe side will do as Damaxx suggested. I have few spare Phoenix contact din rail relays which will do nicely.
     
    grssll, Nov 22, 2018
    #5