Ceiling Fan Control

Discussion in 'Standard Products' started by DDirk, Nov 16, 2009.

  1. DDirk

    DDirk

    Joined:
    Nov 16, 2009
    Messages:
    13
    Likes Received:
    0
    Location:
    usa
    Can some tell me if they is such a device that allows ceiling fan speed and direction control via C-bus?
    If so is it a C-Bus device or is it done with a relay module and discrete capacitors?

    DDirk
     
    DDirk, Nov 16, 2009
    #1
  2. DDirk

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    There is no native C-Bus device dedicated for ceiling fans. Most people do it using the supplied capacitor block wired into a few channels on a standard relay and then using either logic or interlocking to link the channels together.
     
    Newman, Nov 16, 2009
    #2
  3. DDirk

    DDirk

    Joined:
    Nov 16, 2009
    Messages:
    13
    Likes Received:
    0
    Location:
    usa
    Fan Direction

    Thank you Newman,

    I take it that to change direction on a single phase fan will require a double pole c/o relay and the rewiring of the stator windings?

    Rgds
    DDirk
     
    DDirk, Nov 17, 2009
    #3
  4. DDirk

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    It would certainly not be a simple job. Your best bet is probably to buy a fan that has a direction selector switch on it, and then wire that switch out externally (will require some mods) to a change-over relay so that you can flip the direction.
     
    Newman, Nov 17, 2009
    #4
  5. DDirk

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    What good timing, just bought a fan and was going to do the reversing as well through C-bus (it does have a switch on it so I can wire that out).

    I will preface this by saying that I have never wired up a fan, the instructions are absolutely crap.

    I think it is like this
    Speed 1 - no cap
    Speed 2 - cap 1
    Speed 3 - cap 2 (it could be the other way around though)
    Code:
                         1.75uf
                  |-----||--------- (2)
          (1)-----|
                  |-----||--------- (3)
                         3.5uf
    
    My question is, if I use a standard relay unit (not change over), one for each speed, what is the result should all three channels come on.

    I suspect, that all three relays on would be slow speed (ie the cap is bypassed).

    If only relays 2 & 3 came on, I think I would get a fourth speed - even faster than speed 3 (cap1 & cap 2 in parallel giving a new capacitance = 5.25uf), or will I damage the motor.

    It would be great to see a small ceiling fan controller, similar size to the blind relay, with reversing functions as well.

    Mick
     
    Last edited by a moderator: Nov 17, 2009
    znelbok, Nov 17, 2009
    #5
  6. DDirk

    Tyrone

    Joined:
    Nov 17, 2009
    Messages:
    4
    Likes Received:
    0
    Location:
    UK
    DDirk

    Newman is correct, in europe we use lots of ceiling fan in both direction
    and to control it via an automation system is a pain.

    Normally one stator is permantly wired and the other is switched,
    you have to bring out all motor winding wires out and switch both with a
    2 pole change over relay (as you said) that is then operated via your automation system, and is best reduced to zero speed before you change direction.

    Tyrone
     
    Tyrone, Nov 17, 2009
    #6
  7. DDirk

    Tyrone

    Joined:
    Nov 17, 2009
    Messages:
    4
    Likes Received:
    0
    Location:
    UK
    You can have 4 speeds as shown below

    Speed 1 - no cap
    Speed 2 - cap 1
    Speed 3 - cap 2
    Speed 4 - cap 1 & 2 (these are in parallel to each other)

    Tyrone
     
    Tyrone, Nov 18, 2009
    #7
  8. DDirk

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Ceiling fans are wired so that a capacitor is in series with the fan motor at slower speeds. Full speed connects the motor directly to the mains. You cannot get more power to the motor than mains allows by just connecting a capacitor in series.

    Off - Open Circuit
    Low - Weedy tiny capacitor letting through a little current
    Medium - Beefy capacitor letting through more juice
    High - Motor connected directly to mains.

    If you connected the two capacitors in parallel with each other, to the motor, you'd get a sort of Medium+ speed, a bit faster than Medium, but not as fast as High.

    A number of the manufacturers use dedicated capacitor blocks, where the weedy and the beefy capacitors are inside a common package with one terminal of each connected together.
     
    Newman, Nov 18, 2009
    #8
  9. DDirk

    Don

    Joined:
    Aug 4, 2004
    Messages:
    429
    Likes Received:
    0
    Location:
    Townsville, Australia
    Well, actually you can in theory. If you add just enough capacitance to resonate with the motor's inductance at mains frequency, then the motor windings will see higher than normal voltage and the fan can actually run faster than with no capacitor.

    Fortunately, fan motors are typically quite lossy so the 'Q' of any resonant circuit is not very high. High voltages might result in premature failure of capacitors or insulation so if in doubt, I would suggest monitoring the voltage across the capacitor (or the fan motor) to make sure all is within manufacturer's specifications.

    I use the same arrangement as Tyrone suggests, and have for years without any problems. It gives me off, plus three distinct and useful speeds.
     
    Don, Nov 18, 2009
    #9
  10. DDirk

    Automan

    Joined:
    Oct 30, 2009
    Messages:
    7
    Likes Received:
    0
    Location:
    NSW
    Fan Speed

    Tyrone is right in what he has said,

    However there are things to consider as Don indicated.

    The Voltage across the caps / use good quality motor run caps not motor start.

    Do not exceed the manufactures capacitance rating for the motor
    so if the maximum is say 5uF then use 2uF, 3uF and both as 5uF.

    There is no problem doing this.

    Cheers
    Automan
     
    Automan, Nov 18, 2009
    #10
  11. DDirk

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    Thanks for the clarification.

    There is a capacitor block, it has two caps in it (three wires) so it is feasible to run two in parallel. As long as a failure of logic wont cause an issue (ie 2 or three channels on) then there is no need for hardware protection.

    Mick
     
    znelbok, Nov 18, 2009
    #11
  12. DDirk

    brett_lynn

    Joined:
    Sep 4, 2004
    Messages:
    44
    Likes Received:
    0
    Location:
    Beaconsfield Vic
    Fan Control

    "edited extract from training manual"

    Fan control is commonly wired a programmed a number of different ways. In this exercise we will use fan
    speed capacitors wires into a relay to control the fan. So consider that the fan was wired as shown in the figure
    below.

    Group Address " Fan "

    12 Ch Relay
    Ch 1 - Fan
    CH 2 - Fan
    Ch 3 - Fan


    To program C-Bus to operate in this configuration, follow the steps below.
    1) Open the 12 channel relay and click on the Turn On tab.
    2) Change the Interlock Channels parameter to 3.
    3) Configure the Turn On Threshold of Channel 1 to 0%.
    4) Configure the Turn On Threshold of Channel 2 to 30%.
    5) Configure the Turn On Threshold of Channel 3 to 70%.
    6) Set Group Address to Fan on channels 1, 2 and 3
    7) Click the OK
    8) In the Input units set the Group Address ?Fan? to be a Dimmer

    Credits : CIS :D

    Personally for me though....
    I prefer to wire the fan directly from the relay ( cbus on / off )
    the fan crontroller is the located in the
    nearest WIR Cupboard etc... (speed control)

    Have 4 Fans at my place and all have been on 2nd speed for the last 2 1/2 years.....

    Cheers All :)
     
    brett_lynn, Nov 19, 2009
    #12
  13. DDirk

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,392
    Likes Received:
    24
    Location:
    Adelaide, South Australia
    Ha ha ha everything I hear says that variable speed control gets used for the first month. After that PEOPLE figure out the speed that works best for them (comfort, noise, etc), and just use that forever after.
     
    ashleigh, Nov 19, 2009
    #13
  14. DDirk

    fleetz

    Joined:
    Nov 21, 2005
    Messages:
    362
    Likes Received:
    9
    Hi Ashleigh,

    In my case about 98% correct. I manually switch our lounge fan to pos 2 in the wet season here (FNQ) but all other fan are set and forget. All speed controllers are buried in WIR, robes, closets etc so they are not an eye sore. C-Bus control the on off.

    I went through all the options and chose the KISS system and it works great...I get my wife to do the switch to Pos 2 and back to 1 at the end of the wet season!!:D Sweet.........!

    Regards,

    Fleetz
     
    Last edited by a moderator: Nov 21, 2009
    fleetz, Nov 21, 2009
    #14
  15. DDirk

    nev25

    Joined:
    Sep 10, 2009
    Messages:
    2
    Likes Received:
    0
    Location:
    Latrobe Valley Vic Australia
    I'M curious as to why you cant simply use a dimmer channel??
     
    nev25, Nov 25, 2009
    #15
  16. DDirk

    Don

    Joined:
    Aug 4, 2004
    Messages:
    429
    Likes Received:
    0
    Location:
    Townsville, Australia
    Hum
     
    Don, Nov 25, 2009
    #16
  17. DDirk

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    That must be the shortest complete post I have seen!

    To elaborate: The problem with using dimmers for fans is that the motor windings will vibrate from the switched voltage from the dimmer. You will be able to hear a hum or buzzing noise.
     
    Darren, Nov 25, 2009
    #17
  18. DDirk

    Don

    Joined:
    Aug 4, 2004
    Messages:
    429
    Likes Received:
    0
    Location:
    Townsville, Australia
    I couldn't waste such a good opportunity :)

    Besides, most of my responses are long-winded, so this goes a little towards balancing my contribution.
     
    Don, Nov 26, 2009
    #18
  19. DDirk

    brett_lynn

    Joined:
    Sep 4, 2004
    Messages:
    44
    Likes Received:
    0
    Location:
    Beaconsfield Vic
    1 down
    250 to go..... ;)
     