Hi All, Brand new to the C-Bus Forum here! I have a question relating to cbus timers. I have a range of cbus product installed including a B&W logic touchscreen. I am fairly familiar with toolkit & piced which are the programs that i used to setup the system. The touchscreen has 20 in-bult logic timers, my problem is that i have used them all. When i initially programmed the system back in 2009 I tried to get the unit logic to do what i wanted with the lighting and other equipment, but i really struggled to do it, so i ended up using the in-built timers through logic instead. [B]My application i'm struggling with right now is as follows: I have a water level sensor that will trigger a bell press on a cbus coupler, If the water level sensor is on for say 5 min, then the pump will come on. However, if the water level sensor only stays on for 2 min, then the timer will re-trigger itself back to 0. The pump will not turn on until the water level sensor has been called for for a full 5 min. Then the same for off function. If the water level sensor is off for say 5 min, then the pump will go off. However, if the water level sensor only stays off for 2 min, then the timer will re-trigger itself back to 0, The pump will not turn off until the water level sensor has not called for water for a full 5 min. The idea of this is that I dont get nuissance switching as the water level rises and falls. e.g. wind ripples on the water surface triggering the sensor every few seconds.[/B] If i had a spare logic timer i could do it, but i dont. I have had a play with the 'delay function' in the piced logic programming wizard, but the delay seems to be more a case of delaying the output rather than the input. Are there any other timers/methods i can use? Kindest Regards