Discussion in 'C-Bus Toolkit and C-Gate Software' started by ananthkrishna, Dec 20, 2011.

  1. ananthkrishna

    ananthkrishna

    Joined:
    Dec 20, 2011
    Messages:
    5
    Likes Received:
    0
    Location:
    hyd
    when i am doing programme 1 relay is not scanning and it doesnt showing serial no and it showing name as yyyyyy like that so i tried old version also it is showing like that so what is the solution and problem
     
    ananthkrishna, Dec 20, 2011
    #1
  2. ananthkrishna

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    About a year ago I had a 12ch relay doing something similar.
    It was still working on the CBus network properly but I couldnt access it with toolkit even though able to access the other 60 devices.
    It had a built in CBus power supply so to test it I removed it from the network and connected just the CNI and burden to the relay, then tried to scan again with toolkit.
    The relay turned out to be faulty and I had it replaced under warranty.
     
    DarylMc, Dec 20, 2011
    #2
  3. ananthkrishna

    ananthkrishna

    Joined:
    Dec 20, 2011
    Messages:
    5
    Likes Received:
    0
    Location:
    hyd
    thanks

    oh k thanks for ur suggestion but i did wat u said still it is like that only not scanning so i also think it is hardwere problem k
     
    ananthkrishna, Dec 21, 2011
    #3
  4. ananthkrishna

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,308
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    I didnt have to remove any of the 240v wiring or the relay to do that test.
    Perhaps you could try connecting to another unit which has a CBus power supply just to rule out anything else.
    Assuming the relay is still working and not under warranty you could try to use learn mode to make some changes if it is still enabled.
     
    DarylMc, Dec 21, 2011
    #4
  5. ananthkrishna

    ananthkrishna

    Joined:
    Dec 20, 2011
    Messages:
    5
    Likes Received:
    0
    Location:
    hyd
    12 ch relay

    on the same phase two relays are working except this relay i think it is hard ware problem
     
    Last edited by a moderator: Jan 18, 2012
    ananthkrishna, Jan 17, 2012
    #5