    I got problem to trigger the scene stored in 12ch high power dimmer using c-bus group address. Can you brief me how to configure it.
     
    thlow, Aug 25, 2004
    #1
  2. thlow

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    To trigger a Scene in the 12-Channel C-Bus Dimmers is exactly the same as remote triggering a Scene in a Neo/Sautrn/Reflection/SceneMaster. If you can remotely trigger a scene there then you can do it here.

    Just configure a Scene as a basic Scene in the 12-channel unit and then assign a Trigger Group and Action Selector for the triggering. Then on your input unit (C-Touch, key unit etc) configure a key to the same Trigger Group and Action Selector value.

    If you are using a standard key unit then you'll need to assign the key unit's primary application to the Control Application $CA and then use a recall to level command with a level that matches the Action Selector value.

    The Advanced Scenes in the unit are a slightly different, so give this a go first so that you understand the concept of what's going on.
     
    Newman, Aug 25, 2004