Bus Controller 5102

Discussion in 'General Discussion' started by Stephen Scott, Jan 3, 2015.

  1. Stephen Scott

    Stephen Scott

    Joined:
    Apr 18, 2014
    Messages:
    17
    Likes Received:
    0
    Location:
    Melbourne
    Bus Coupler 5102

    How do you program a Bus Controller when it is connected across a dry relay contact,
    Relay closed = C Bus Relay contact closed - Fan on
    Relay open = C Bus Relay contact open after 5 minute run on timer - Fan off .

    I am obviously over thinking this as I can get the fan to turn on when the relay is closed but it doesn't turn off when the relay contact opens!

    Any assistance would be appreciated.

    Regards
    Stephen
     
    Last edited by a moderator: Jan 3, 2015
    Stephen Scott, Jan 3, 2015
    #1
  2. Stephen Scott

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,580
    Likes Received:
    188
    Location:
    Adelaide, Australia
    On a short press select the ON command. On both short and long release select a timer with an OFF KEY expiry command and set the required timeout.
     
    Last edited by a moderator: Jan 3, 2015
    Ashley, Jan 3, 2015
    #2
  3. Stephen Scott

    Stephen Scott

    Joined:
    Apr 18, 2014
    Messages:
    17
    Likes Received:
    0
    Location:
    Melbourne
    Bus Coupler

    Ashley,

    Thanks for putting me on the right track, really simple now that you have shown me.
    I did however need to use "Timer" instead of "Bell Press" to Retrigger the Time out function.

    Thanks again.

    Stephen
     
    Stephen Scott, Jan 4, 2015