    Hi.

    I had previously been pulsing the relevant group to 100% for 2 seconds using logic, which worked fine, but doing the same thing in scheduler doesn't work to open the blinds at sunrise.

    Scheduler closes the blinds ok, just won't open them.

    Is there some quirk I could be missing?
     
    Tension, Jun 21, 2026
    #1
  2. Tension

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,663
    Likes Received:
    226
    Location:
    Adelaide, Australia
    What blind controller are you using?
     
    Ashley, Jun 21, 2026
    #2
  3. Tension

    Tension

    Joined:
    Apr 30, 2015
    Messages:
    200
    Likes Received:
    6
    Location:
    Belfast
    Shutter relay
     
    Tension, Jun 21, 2026
    #3
  4. Tension

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,663
    Likes Received:
    226
    Location:
    Adelaide, Australia
    With the shutter relay you set it to 100% to open and 0% to close. The relay will operate for the fail safe time which you normally set to how long the blinds take from fully closed to fully open. This also allows you to set the blind at any percentage. The shutter relay assumes the blind motor has limit switches.
    If the shutter relay is in level translation mode several values are interpreted as toggle commands. These are:
    1% Alternate between close and stop (2 button operation)
    2% Stop
    98% Alternate between open, stop, close, stop (one button operation
    99% Alternate between open and stop (2 button operation)

    I set mine on a single button when log press is toggle (open/close) and short press is stop.

    If you pulse it for 2 seconds it will start to open for 2 seconds then close. If it was working in logic then the pulse wasn't happening.
     
    Ashley, Jun 21, 2026
    #4
  5. Tension

    Tension

    Joined:
    Apr 30, 2015
    Messages:
    200
    Likes Received:
    6
    Location:
    Belfast
    I had modified a Somfy remote to work off the open/close/common terminals on the relay. I only use 2 seconds because sometimes the blinds don't respond to a rapid button press. It keeps sending the open or close command if you hold the button I found. So I set 2 secs as the maximum time in Toolkit.

    Anyway, it's been working for weeks with logic on the PAC, just not with the scheduler.

    Weird.
     
    Tension, Jun 21, 2026
    #5
  6. Tension

    Tension

    Joined:
    Apr 30, 2015
    Messages:
    200
    Likes Received:
    6
    Location:
    Belfast
    Screenshot attached
     

    Attached Files:

    Tension, Jun 22, 2026
    #6
  7. Tension

    Tension

    Joined:
    Apr 30, 2015
    Messages:
    200
    Likes Received:
    6
    Location:
    Belfast
    Aaah. Final level was set to "OFF". Gonna change it to "ON" and see if that fixes it...
     
    Tension, Jun 22, 2026
    #7
  8. Tension

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,663
    Likes Received:
    226
    Location:
    Adelaide, Australia
    So you aren't actually using the shutter relay to control the blinds as designed, you are using it to press a remotes buttons. Information like this is critical if you want useful responses :)
     
    Ashley, Jun 22, 2026
    #8
    Tension likes this.
  9. Tension

    Tension

    Joined:
    Apr 30, 2015
    Messages:
    200
    Likes Received:
    6
    Location:
    Belfast
    In case anyone else comes across the same issue, I changed it from pulse to ramp to 0% or 100% immediately and that fixed it.

    Thanks again Ashley, single handedly doing C-bus tech support for the entire planet, you should be getting paid for this :)
     