Air Conditioning Integration

Discussion in 'General Discussion' started by jay, Feb 9, 2006.

  1. jay

    jay

    Joined:
    Nov 2, 2004
    Messages:
    51
    Likes Received:
    0
    Location:
    Brisbane
    Just wanted to get some feedback on eveyone's experiences with controlling AC with C-Bus.
    Positive or negative.
    Brands that work - brands that don't.
    Levels of control ie: relays, RS232, high level C-Bus interface, PC control (thru Homegate, Schedule Plus)
    Tell us your story...
     
    jay, Feb 9, 2006
    #1
  2. jay

    jay

    Joined:
    Nov 2, 2004
    Messages:
    51
    Likes Received:
    0
    Location:
    Brisbane
    Hmmm,
    It seems as though no-one has done any AC integration with C-Bus or if they do have any experience or information, it is so sensitive that it can't be shared on these forums. (60+ views to this topic & not 1 reply)
    Our limited experience has involved Daikin but after the client decided the Daikin/C-Bus interface was far too expensive we resorted to simple ON/OFF control by using C-Bus volt free relay contacts connected to an external timer overide terminal on the fan core unit. Pretty limited integration :(
    We have a few upcomming projects that require AC integration to which we would like to offer a better solution. Hopefully someone in the C-Bus community (Clipsal techies at least) can point us in the right direction for successful integration of C-Bus with AC control.'
    Cheers
     
    jay, Feb 13, 2006
    #2
  3. jay

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    AC Integration is certainly a bit of a grey area. IMHO a lot of it comes down to the lack of widely adopted interfacing standards. Sure there are standards, they're just not widely adopted.

    We've seen quite a few AC systems integrated through IR and a few others through serial control on a case-by-case basis involving the integrator coming up with something tricky. Others have been, as you say, through basic on/off control or some form of dry contact input wired up to C-Bus relays.
     
    Newman, Feb 13, 2006
    #3
  4. jay

    JohnC

    Joined:
    Apr 6, 2005
    Messages:
    554
    Likes Received:
    1
    Location:
    Sydney
    I can only offer generalised comments, as I am definitely no expert at this. From what I've seen, it's as Newman said - a problem / limitation on the A/C side, not really of Cbus's capabilities.

    The A/C companies make controllers, and those ensure all the operational characteristics are covered (eg: compressor motor restart delays, etc). It would be quite painful finding out and then recreating those in your own control system. So, I guess you might be asking for an I/O interface.

    All decent A/C controllers offer timers, etc - What operational benefit does integration with Cbus provide you with?

    Sorry for the dumb question - as far as I am concerned an A/C is simply switched on and then a thermostat controls the temperature. If you want it to only operate it between 9.00am and 9.00pm, then you set the timer on the unit accordingly. If you want telephone control, then you buy that from the A/C manufacturer.

    I guess I am having trouble understanding what exactly there is to "control" on it... the thermostat automatically controls the temperature, and it's not the kind of thing that you'd run off a IR sensor, etc... ??? :confused:

    JC (showing my ignorance)
     
    JohnC, Feb 13, 2006
    #4
  5. jay

    RossW

    Joined:
    Oct 10, 2005
    Messages:
    118
    Likes Received:
    0
    I don't suppose you'd consider turning the A/C off during (extended) unattended periods a benefit?

    Or perhaps different setpoints depending on time of day, or season, or occupied status?

    I know in my old place (which didn't have c-bus) I used to have a greater deadband during transitional seasons, pulled the temperature down a little more at bedtime, allowed it to get hotter inside if the place wasn't occupied (but not completely turned OFF).

    Zone motors that allow a ducted system to put the air where it's needed most (based on what the system can see in terms of occupancy, or if you wanted to be really smart - increase the A/C airflow if you have 1200W of lights on in a room!)

    There are any number of reasons why one could/would want to have more control than "on/off". I know, I certainly would (if I weren't built underground and have no need of aircon!)

    RossW
     
    RossW, Feb 13, 2006
    #5
  6. jay

    fleetz

    Joined:
    Nov 21, 2005
    Messages:
    362
    Likes Received:
    9
    I am intrested in the "Daikin/C-Bus interface" mentioned in your post. Is there some more detail you can provide on it? Is it a Daikin C-Bus interface ie Daikin have developed it or is there a 3rd party device out there?

    Thanks,

    Fleetz
     
    fleetz, Feb 13, 2006
    #6
  7. jay

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    I have just launched into trying to get serial control of a carrier system. I have obtained a copy of their indoor weather sation software and will have to reverse engineer it, but it is slow going as I am no expert at this stuff.

    It is very difficult to find information for AC integration indeed. Even the guys at carrier dont seem to know that much about it for residential systems. As for commercial systems, thats a different story.

    Mick
     
    znelbok, Feb 13, 2006
    #7
  8. jay

    jay

    Joined:
    Nov 2, 2004
    Messages:
    51
    Likes Received:
    0
    Location:
    Brisbane
    The interface I installed (about 18 mths ago) was for an E-Bos (Lonworks) job & I can't recall too much about it but do remember that Daikin said that the same interface was being used in C-Bus installations. I have the manual around here somewhere & if I find it I will post more deatils.
     
    jay, Feb 13, 2006
    #8
  9. jay

    jay

    Joined:
    Nov 2, 2004
    Messages:
    51
    Likes Received:
    0
    Location:
    Brisbane
    I'm hearing you RossW....

    My position on this topic is for more than basic C-Bus lighting/device control - more emphasis on INTEGRATION ie: different systems communicating to each other which leads to my goal of offering single point control of the home. To acheive this (in the scope of this thread) I need to know AC status (current set point, fan speeds, zones etc.) to offer the end user the ability to make a choice or for my programming (in a touch screen or Homegate for example) to control a device accordingly.
     
    jay, Feb 13, 2006
    #9
  10. jay

    Sergio

    Joined:
    Apr 18, 2005
    Messages:
    28
    Likes Received:
    0
    I told about integration with Daikin guys from my region stuff, and they said that there are only two legal ways for Daikin integration.
    First way is to use IR control.
    Second way is to use Daikin LON interface (two or more thousands $$).

    Daikin has serial interface for AC, but dont provides any specification or documentation about. This serial interface only for use with Daikin PC software.

    Maybe you would have more luck with Mitsubishi, which has optional serial interface fore some of its AC units with open specification.
     
    Last edited by a moderator: Feb 25, 2006
    Sergio, Feb 25, 2006
    #10
  11. jay

    Nobes

    Joined:
    Oct 7, 2004
    Messages:
    164
    Likes Received:
    1
    Location:
    Hobart
    Mick,

    Would be very interested if you have any luck with the carrier system, trying to get info out of those guys is difficult at the best of times.
     
    Nobes, Feb 26, 2006
    #11
  12. jay

    GlenF

    Joined:
    Jan 22, 2006
    Messages:
    130
    Likes Received:
    0
    I have just integrated an A/C unit into my home automation setup. I used an actron a/c unit but bought a separate zone control system from the US (A company called RCS - www resconsys.com). This controller has individual thermostats in each room so you can set different setpoints for each room and the controller controls the airflow to achieve the correct temperature. It can even revert to heating in another room once the cooling has finished.

    The RCS unit (ZC6R) has a RS232 or RS 485 interface and I plug it into my home automation controller (Homevision - www.csi3.com). The homevision has the ability to control C-bus output devices. I have not done this yet but I do not believe it will be difficult.

    The Homevision controller has access to all the parameters and controls for the A/C and it can all be adjusted via the internet or locally via a flash movie that I use on a touchscreen LCD.

    This probably does not help a great deal but I thought some may be interested in how it can be done.


    Glen
     
    GlenF, Mar 8, 2006
    #12
  13. jay

    Andrew

    Joined:
    Dec 17, 2004
    Messages:
    21
    Likes Received:
    0
    Location:
    Brisbane
    AC control

    Has any more information come about from this posting or has anyone had a play with it. I have 2 Daikin related jobs coming up (customer chose Daikin on our recommendation due to CIS advise) and I was assured by CIS Reps prior to the PICED release, that this would be an easy do. (i.e. Managing the AC functions from the touch screen.) Well... I'm not sure about the 'easy' any more. I am still in very early stages of learning RE. building code etc as we are just starting to install these units in jobs priced up some time ago. I get that this is possible but am feeling very green and am fearful of disappointing customers. Would be grateful to anyone who is willing to share ideas or set me in some sort of direction... My lesson? ? Research before commitment!:confused:
     
    Andrew, Mar 16, 2006
    #13
  14. jay

    470

    Joined:
    Mar 22, 2006
    Messages:
    3
    Likes Received:
    0
    any updates on this A/C control subject ???
     
    470, Aug 1, 2006
    #14
  15. jay

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    AdvantageAir (www.advantageair.com.au) have a C-bus interface in beta at the moment.

    I am meeting with the rept his afternoon to talk about it some more.

    mick
     
    znelbok, Aug 1, 2006
    #15
  16. jay

    daniel C-Busser Moderator

    Joined:
    Jul 26, 2004
    Messages:
    766
    Likes Received:
    20
    Location:
    Adelaide
    On the general topic of Brands that Work, Brands that Don't...

    It appears that at least some Fujitsu air-conditioners don't integrate well, based on my own communication with them about the AOT30RMBL, their highest-capacity residential ducted reverse-cycle air conditioner.

    -----Message 1-----
    From: Daniel
    Sent: Monday, 5 June 2006 4:46 PM
    To: Fujitsu
    Subject: Fujitsu Integration

    Hello,

    I'm investigating the installation of the Fujitsu AOT30RMBL system (with the standard weekly timer keypad that comes with it).

    What means of integration are possible if I wish to control the A/C from a home automation system, for example Clipsal C-Bus? Are there RS-232 serial, infrared or other means of interfacing with the keypad?

    Thanks,
    Daniel

    -----Message 2-----
    From: Fujitsu
    Sent: Thursday, 8 June 2006 9:56 AM
    To: Daniel
    Subject: RE: Fujitsu Integration

    Good Morning Daniel,

    Unfortunately there is no means of home automation integration.

    The airconditioner has a control system unto itself that cannot be altered or controlled from an outside device such as a Clipsal system.

    We do have some of our larger systems that will allow a degree of controls integration but unfortunately the system you have will not allow.

    The only way to control this system externally is to switch the power supply and rely on the Auto Restart to start the airconditioner in the Previously set setting.

    I hope this explains the situation and please let me know if you have any further questions,

    Kind Regards

    [Name removed]
    Manager - Product Development Department
     
    daniel, Aug 2, 2006
    #16
  17. jay

    Sergio

    Joined:
    Apr 18, 2005
    Messages:
    28
    Likes Received:
    0
    Control Daikin split

    Splits from Daikin can be controlled by means optional Daikin unit KRP413A1S. Features are not reach, but you can switch unit off and on with C-Bus relays.
     
    Sergio, Aug 8, 2006
    #17
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.