5753PEIRL in Light Maintenance

Discussion in 'C-Bus Wired Hardware' started by Colin Smith, Aug 1, 2019.

  1. Colin Smith

    Colin Smith

    Joined:
    Aug 3, 2004
    Messages:
    102
    Likes Received:
    0
    Location:
    Auckland, New Zealand
    We have a new Library install where the supplied spec is to use C-Bus Saturn switches, SHAC and touch screen to control DALI Lighting. We will be using 5753PEIRL for light maintenance in parts of the library.

    I have not used the 5753PEIRL for light maintenance before and I am unable to find notes on how to set this up. (Fine for its other function but not Light Maintenance.)

    I currently have a basic system setup on my desk to test the basic operation. I have set a base level for the wanted lux level and placed a sheet of paper over the sensor to simulate light level change. (DALI Gateway is set to match ramp rates).

    I am expecting to see light level changes to take place over 4 seconds. This I see when watching the application log but before the 4 second time period has passed there is a group ramp to xxx over 0 seconds. This then seems to cause the system to hunt. I would have expected to see the hunt messages to be ramps over 4 seconds not o seconds.

    What is causing the ramp over 0 seconds?

    I assume at this stage I am missing something. Do I need to set a pot to set a level and if so what is the procedure for doing so in the final install.

    DateTime= 2/08/2019 07:35:37.143 App= 095 DALI Group= 000 Light Group 01 Unit= 029 SENPILL/NEWUNIT Event= Group ramped to 255 (100%) over 4 seconds

    DateTime= 2/08/2019 07:36:00.551 App= 095 DALI Group= 000 Light Group 01 Unit= 029 SENPILL/NEWUNIT Event= Group ramped to 001 ( 1%) over 4 seconds

    DateTime= 2/08/2019 07:36:01.319 App= 095 DALI Group= 000 Light Group 01 Unit= 029 SENPILL/NEWUNIT Event= Group ramped to 210 ( 83%) over 0 seconds

    DateTime= 2/08/2019 07:36:05.543 App= 095 DALI Group= 000 Light Group 01 Unit= 029 SENPILL/NEWUNIT Event= Group ramped to 255 (100%) over 4 seconds

    DateTime= 2/08/2019 07:36:12.823 App= 095 DALI Group= 000 Light Group 01 Unit= 029 SENPILL/NEWUNIT Event= Group ramped to 001 ( 1%) over 4 seconds

    DateTime= 2/08/2019 07:36:13.559 App= 095 DALI Group= 000 Light Group 01 Unit= 029 SENPILL/NEWUNIT Event= Group ramped to 211 ( 83%) over 0 seconds

    DateTime= 2/08/2019 07:36:17.799 App= 095 DALI Group= 000 Light Group 01 Unit= 029 SENPILL/NEWUNIT Event= Group ramped to 255 (100%) over 4 seconds

    DateTime= 2/08/2019 07:36:25.063 App= 095 DALI Group= 000 Light Group 01 Unit= 029 SENPILL/NEWUNIT Event= Group ramped to 001 ( 1%) over 4 seconds

    DateTime= 2/08/2019 07:36:25.767 App= 095 DALI Group= 000 Light Group 01 Unit= 029 SENPILL/NEWUNIT Event= Group ramped to 213 ( 84%) over 0 seconds
     
    Colin Smith, Aug 1, 2019
    #1
  2. Colin Smith

    Wonkey

    Joined:
    Aug 3, 2004
    Messages:
    395
    Likes Received:
    37
    Location:
    Adelaide
    The 0 sec command happens when the light level has been achieved hence if the output is at level 83% then a command ramp to 83% over 0 seconds would hold that level.
    In Toolkit ensure you have a reasonable margin set on the light level tab I would suggest at least 10%.
    Colin
     
    Wonkey, Aug 2, 2019
    #2