5500AC2 Weird Issue with DALI Lights & Scheduling

Discussion in 'C-Bus Automation Controllers' started by IJED_Mitch, Jun 2, 2026.

  1. IJED_Mitch

    IJED_Mitch

    Joined:
    Jun 2, 2026
    Messages:
    1
    Likes Received:
    0
    Location:
    Nowra, NSW Australia
    I'm currently stuck with an odd issue where i've got 2 x group address that randomly turn off at random times of an afternoon that occurs every day.
    One group address is DALI controlled lighting and the other is a relay channel.

    For some reason in the 5500AC2 logs, it shows each group suddenly ramps down to OFF over 12 seconds. Which I have no programming whatsoever for ramping down the lights. All the DALI lights on the group address are purely controlled via a Schedule to turn on and off within the 5500AC2 and the DALI gateway.
    No other input devices control these DALI lights.

    Also what is very strange is that the logs show that 'Sporties Sign (46)' group address, ramps down over 12s. Whereas its on a 16 channel Spacelogic relay? So in theory It cannot ramp down.

    I've attached a log file from the Application Controller showing the logs for the particular group address: 'Outdoor GM Row-1'(47) all times of the issue occurring have been highlighted.

    Any help would be greatly appreciated.
     

    Attached Files:

    IJED_Mitch, Jun 2, 2026
    #1
  2. IJED_Mitch

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,667
    Likes Received:
    226
    Location:
    Adelaide, Australia
    Run the diagnostic utility. It will tell you the source unit that sent the command.
     
    Ashley, Jun 2, 2026
    #2
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.