View Full Version : Change DLT Lable Variant Via Logic
xrmichael
02 Jan 10, 12:28 AM
I have been using the following command via HG to change DLT labels:-
SetStringIBSystemIO("Label Group Text", 254, 56, "WIN BED 4", 0, 'Vlux Open');
This has worked fine, until we have alter some other key lables to a custom font size, now the labels changed by HG are at a different size to the rest.
So the question is can the above command be altered to set the font size along with the text.
Or
I have made 2 variants for the group in question 1-Vlux Open 2-Vlux Closed is there a way to make the dlt alter the variant displayed via logic ?
Michael
ashleigh
02 Jan 10, 01:01 PM
No sir!
If you set a text label you get whatever the font size is.
If you set a custom font / size at commissioning time, its actually loaded into the unit as a bitmap image.
ie.... custom = bitmap image.
standard text = whatever the font + size is that delivers text. Irrespective of where that setting is originated in the network.
xrmichael
02 Jan 10, 06:38 PM
Sorry for being a bit slow but the xmas partying has left my head a bit scrambled, to get it straight in my head.
So if you alter the label text via logic with the command above you can only use 1 font and size.
And you cannot get the dlt to swap to a different variant via logic on the fly
Newman
02 Jan 10, 07:29 PM
So if you alter the label text via logic with the command above you can only use 1 font and size.
And you cannot get the dlt to swap to a different variant via logic on the fly That's correct.
As Ashleigh says, any custom font size/style is implemented in the DLT as a bitmap. Only the default font size/style is treated as text. When HG bashes out the new label it is sent across the bus as a text string, which the DLT applies the default font/style to when displaying. The DLT has a fairly small processor and having enough memory and grunt to run all the fancy font footwork would definitely push the price up.
You can't switch variants from within HG. It's a Toolkit-commissioning setting in the DLT on a per-unit basis.
xrmichael
02 Jan 10, 07:40 PM
And I take it there is no way to alter the default font in the dlt ?
Newman
02 Jan 10, 07:47 PM
Nope, it's compiled into the code that runs in the graphics processor.
Do the public docs for labelling explain how to send a label bitmap over the bus? If so, then you may be able to do it that way.
Clinton's Electrical
04 Jan 10, 07:26 AM
Hi Guys in Response To the Above Post, i Think What The Chap Is Trying To Do is Similar To Dynamic 1 And Dynamic 2 in The MARPA Software. ThisWOULD Be Handy For Blinds in Future:D.. Changing Subject Anyone Know of A Way To Select A Group Address On A PACA Controller. What i Trying To Do is Set Up 1 Button For Say Eg 10%= GA1 20%=GA2 30%=GA3 Etc... I Have DLT's And Neo's And c2000 Input units And A Paca Controller. Ps GA 1 Is Ir Command FM Tuner GA 2 Is CD GA 3 Is TV Audio Etc All Sent From A NIRT.Thanks Guys And Happy New Year ...:)