Hi,
I noticed a few times that my Comfort system sometimes changes to the wrong date. Tonight I actually simulated this after a project download via PICED.
When doing a project download, one of the options are to set the Date & Time. Usually you set this to make sure that your PAC is running the right time and date.
After a transfer my Comfort panel changed from year 09 to year 29. The output below is from Comfigurator's Monitor window showing, firstly, setting the time & date back to normal using Comfigurator and then doing a Date & Time setting using PICED connected via USB to the PAC.
Setting Date & Time via Comfigurator.
> DT20090930184247
< DT20090930184247
Doing a Set Date & Time from PICED 4.7.1.
< DT51290930194326
< DT51290930194300
< DT51290930194300
Am I the only one time travelling to the year 5129??? Seems a lot like 2009 to me :-) I don't know if this is an incorrect command sent to Comfort via PICED or is the command interpreted wrong by the UCM/CBus connecting the two units together. I presume it's the UCM/CBus because below is the log entry for PICED (running on a second PC for capture purposes)
2009/09/30 19:43:31 Date/Time: Received C-Bus message to set date to 2009/09/30
2009/09/30 19:43:31 Date/Time: Received C-Bus message to set time to 19:43:31
2009/09/30 19:43:31 Date/Time: Received C-Bus message to set time to 19:43:31
2009/09/30 19:43:32 Date/Time: Received C-Bus message to set time to 19:43:32
2009/09/30 19:43:32 Date/Time: Received C-Bus message to set time to 19:43:32
Can anyone confirm my findings?
Thanks,
Ingo
I noticed a few times that my Comfort system sometimes changes to the wrong date. Tonight I actually simulated this after a project download via PICED.
When doing a project download, one of the options are to set the Date & Time. Usually you set this to make sure that your PAC is running the right time and date.
After a transfer my Comfort panel changed from year 09 to year 29. The output below is from Comfigurator's Monitor window showing, firstly, setting the time & date back to normal using Comfigurator and then doing a Date & Time setting using PICED connected via USB to the PAC.
Setting Date & Time via Comfigurator.
> DT20090930184247
< DT20090930184247
Doing a Set Date & Time from PICED 4.7.1.
< DT51290930194326
< DT51290930194300
< DT51290930194300
Am I the only one time travelling to the year 5129??? Seems a lot like 2009 to me :-) I don't know if this is an incorrect command sent to Comfort via PICED or is the command interpreted wrong by the UCM/CBus connecting the two units together. I presume it's the UCM/CBus because below is the log entry for PICED (running on a second PC for capture purposes)
2009/09/30 19:43:31 Date/Time: Received C-Bus message to set date to 2009/09/30
2009/09/30 19:43:31 Date/Time: Received C-Bus message to set time to 19:43:31
2009/09/30 19:43:31 Date/Time: Received C-Bus message to set time to 19:43:31
2009/09/30 19:43:32 Date/Time: Received C-Bus message to set time to 19:43:32
2009/09/30 19:43:32 Date/Time: Received C-Bus message to set time to 19:43:32
Can anyone confirm my findings?
Thanks,
Ingo