View Full Version : Schedule Plus saved states


Robbo
21 May 07, 09:00 AM
I have a site that is running schedule plus on a networked PC. After a reboot due to a power outage, I would like a number of "PIR enable" buttons to default to the enable state.
I have tried saving the program with the buttons in the required state but this does not work.
HELP!!

Darren
21 May 07, 12:38 PM
Are these "PIR Enable" buttons you refer to Schedule Plus buttons controlling C-Bus ?

If so, you can restore the state of them to the previous state (before the power failure) by using the Power Failure Recovery feature (see help file).

If you want the C-Bus level to be set to a particular state on power-up, regardless of what it was previously, just set the level in the logic Initialisation section.

Robbo
21 May 07, 04:19 PM
Thanks that helps!

Age
21 May 07, 05:47 PM
Another option is to put the Enable/Disable group address into a spare channel on a relay or dimmer, this also fixes the problem. That way the MMI has a reference to the physical state of that group address in the output unit.

So when the network powers up, it will see the enable / disable GA is on or off and the level of the group in the PIR will be accurate.

Age