As many of you know, transformers and Cbus are a bit of a passion for me :-)
Following questions asked here, I looked further into ways of solving the Capacitive Loading presented by Electronic Transformers to Cbus Leading Edge Dimmers.
Most of the technical info you need to know about is on the 2 x PDFs linked off this page of the new CIS website :
http://www2.clipsal.com/cis/technical/technical_support/newsletters_and_faq/transformers
Which is fine, but those PDFs tend to gloss over "why" there is a problem (which is outside the scope of this post), or to offer a clear and easy to understand solution. But you know what... the answer is actually hidden in there...
What about the (common) situations where the client has already purchased a heap of "high capacitance" transformers? The answer lies with the Clipsal 32EIND Inductor. For every 2A of load, you need one - it is connected in SERIES with the Active between the output of the dimmer and the transformers.
Basically, in a nutshell - the 32EIND blocks all the nasty capacitance from attacking and killing your Cbus Dimmers :eek:
From Clipsal Product FAQ's :
Q: What load can a 32EIND carry?
A: 32EIND can only handle a 2A load because of the limitations of the inductor.
When larger loads are required to be controlled, you need to provide separate 2A feeds, and multiple 32EIND devices.
- The 32/2400 10A leading edge Dimmer can connect 5 x 32EIND (each 32EIND drives up to 2A load)
- The 32/1000 4A leading edge Dimmer can connect 2 x 32EIND (each 32EIND drives up to 2A load)
So, if you want to use a big Pro Dimmer and run lots of trannies off it, you segregate them into "groups" of under 2A, and use one 32EIND for each group.
It's not rocket science to work out how many to use, or to connect them up to your loads. Providing you can split the loads, which might present a problem in some installations...
The other (maybe easier and neater) alternative is to use a 4 channel Pro Dimmer, which allows 1000nF Capacitance on each channel. By setting all 4 channels with the same Group Address, you can dim them in tandem yet spread the capacitance. So, you can connect 4 x 5A (each 1000nF) 4000nF total , instead of only 1000nF for a 20A 1 channel - does that make sense?
I hope that helps - feel free to ask questions etc if required.
And CIS people, please confirm that the information I have stated above is correct.
John
Edited to fix mistakes identified by Wonkey :)
Following questions asked here, I looked further into ways of solving the Capacitive Loading presented by Electronic Transformers to Cbus Leading Edge Dimmers.
Most of the technical info you need to know about is on the 2 x PDFs linked off this page of the new CIS website :
http://www2.clipsal.com/cis/technical/technical_support/newsletters_and_faq/transformers
Which is fine, but those PDFs tend to gloss over "why" there is a problem (which is outside the scope of this post), or to offer a clear and easy to understand solution. But you know what... the answer is actually hidden in there...
What about the (common) situations where the client has already purchased a heap of "high capacitance" transformers? The answer lies with the Clipsal 32EIND Inductor. For every 2A of load, you need one - it is connected in SERIES with the Active between the output of the dimmer and the transformers.
Basically, in a nutshell - the 32EIND blocks all the nasty capacitance from attacking and killing your Cbus Dimmers :eek:
From Clipsal Product FAQ's :
Q: What load can a 32EIND carry?
A: 32EIND can only handle a 2A load because of the limitations of the inductor.
When larger loads are required to be controlled, you need to provide separate 2A feeds, and multiple 32EIND devices.
- The 32/2400 10A leading edge Dimmer can connect 5 x 32EIND (each 32EIND drives up to 2A load)
- The 32/1000 4A leading edge Dimmer can connect 2 x 32EIND (each 32EIND drives up to 2A load)
So, if you want to use a big Pro Dimmer and run lots of trannies off it, you segregate them into "groups" of under 2A, and use one 32EIND for each group.
It's not rocket science to work out how many to use, or to connect them up to your loads. Providing you can split the loads, which might present a problem in some installations...
The other (maybe easier and neater) alternative is to use a 4 channel Pro Dimmer, which allows 1000nF Capacitance on each channel. By setting all 4 channels with the same Group Address, you can dim them in tandem yet spread the capacitance. So, you can connect 4 x 5A (each 1000nF) 4000nF total , instead of only 1000nF for a 20A 1 channel - does that make sense?
I hope that helps - feel free to ask questions etc if required.
And CIS people, please confirm that the information I have stated above is correct.
John