PDA

View Full Version : Loss of Network Connection Help Needed


Panash
13 Sep 04, 10:05 PM
I Have a 5500PC PC interface connected via a L5508D1A Dimmer unit to a 5034NL 4 Key input unit as a training exercise and lost communications with the Network after experimenting with adding a L5512RVFP to the mix and possibly incorrectly saving changes to the network.
When scanning the network the unit comms light flashes and returns a message "Could Not Get Project Name" appears along with "Unknown Error".
I appreciate any help I can get at this early stage of endeavour.
Thanks
Paul.

Newman
14 Sep 04, 09:29 AM
Paul

Sounds like you either have a network burden issue or the L5512RVFP has the same unit address as your PCI.

If you don't have a network burden enabled anywhere please do so and try moving the PCI to a different unit address too.

Panash
14 Sep 04, 02:30 PM
Thanks Newman,
I managed to activate the burden on the PCI and get the local network to scan and identify all units except the L5512RVFP. The network does not acknowledge that the unit is connected.
Thanks
Paul

UncleDick
16 Sep 04, 05:41 PM
As Newman says the 12 ch has probably got the same Unit Address as the PCI so highlight the PCI and then go to the change Unit Address button to the top of the screen (shows a hand holding a pen) follow the ok buttons and you should find that the 12 ch is revealed.

Panash
16 Sep 04, 07:16 PM
Thanks UncleDick,
All better now! Lesson learnt, sometimes things are simpler than they first appear. :)
All the best
Paul