View Full Version : C-Gate lighting strange issue
nickrusanov
03 Sep 04, 07:59 PM
Does anyone know about next issue:
If C-Bus is connected to C-Gate, once in 300 sec. DSI gateway makes lights dimm down 10-12% on 1-2 sec. Pretty unusual and not very pleasant for my integrator in Novosibirsk, having C-Bus installed in Concert hall.
Thank you
Darren
06 Sep 04, 01:37 PM
If C-Bus is connected to C-Gate, once in 300 sec. DSI gateway makes lights dimm down 10-12% on 1-2 sec. Pretty unusual and not very pleasant for my integrator in Novosibirsk, having C-Bus installed in Concert hall.
We have not come across this problem before.
I assume that this problem does not occur if C-Gate is not running ?
Can you tell us the version of C-Gate ?
Can you get a C-Gate log showing the messages at the time of the lights dimming ? This would be a lot of help.
John Harnett
09 Sep 04, 10:42 AM
Does anyone know about next issue:
If C-Bus is connected to C-Gate, once in 300 sec. DSI gateway makes lights dimm down 10-12% on 1-2 sec. Pretty unusual and not very pleasant for my integrator in Novosibirsk, having C-Bus installed in Concert hall.
Thank you
It may not be related but I experience this when ever I request the DSI gateway status from the prgramming GUI.
John
Newman
12 Nov 04, 08:32 AM
Gents
An updated version of C-Gate has been released that addresses this issue. It is available for download here:
http://www.clipsal.com/cis/downloads.php3#CGate
You will need to have C-Gate 1.5 installed first and then download and install the 1.5.3 update.